read PM8000 at pos

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • read PM8000 at pos
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
YunusArat
Lieutenant | EcoXpert Master YunusArat Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2025-04-13 11:07 PM

0 Likes
4
236
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-13 11:07 PM

read PM8000 at pos

Hi

Can I read PM8000 at power operation studio with ready drivers?

 

Where its driver?

 

YunusArat_0-1744610761754.png

 

Labels
  • Labels:
  • PM8000
Tags (3)
  • Tags:
  • english
  • pm8000
  • pos2024
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2025-04-14 06:34 AM . Last Modified: ‎2025-04-14 06:38 AM

1 Like
1
192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-14 06:34 AM

Hi @YunusArat , 

PM8000 is native to Power Operation.

There is a default PM8000 Device Profile based on ION protocol.

 

Please use the "Set Up Project" tab on the Profil Editor.

 

Romain_Polette_0-1744637609680.png

 

Do not forget to export your project before exiting Profile Editor.

 

Once PM8000 profile added to your project, you can create a PM8000 I/O Device thanks to the I/O Device Manager.

Romain_Polette_1-1744637918345.png

 

Regards, 

 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2025-04-16 06:42 AM

1 Like
0
130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-16 06:42 AM

Hello @YunusArat , 

Panel Server is not compatible with ION Protocol.
PM8000 connected through Modbus Serial is native to PAS600 and PAS800. Please check at least your PM8000 COM1 parameters are aligned with the Serial parameters of the Panel Server (8E1 by default). At this level you must be able to read PM8000 Modbus Registers through the "Register Read" feature of the Panel Server.

 

EcoStruxure Power Operation has no Modbus Device Profile for PM8000. You have to create one based on the PM8000 Modbus Map and EPO PwrModbus driver.

For better integration, it is strongly recommended to connect your PM8000 to EPO through ION Ethernet.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 4
RobGraham
Commander RobGraham Commander
Commander

Posted: ‎2025-04-14 05:51 AM

2 Likes
0
199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-14 05:51 AM

There is already a device profile under "Create Device Profiles" called "PM8000 Standard".  It uses the ION device type like the other ION meters.

 

In the future, you may want to post these types of questions on the EcoStruxure Power Operation board.

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2025-04-14 06:34 AM . Last Modified: ‎2025-04-14 06:38 AM

1 Like
1
193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-14 06:34 AM

Hi @YunusArat , 

PM8000 is native to Power Operation.

There is a default PM8000 Device Profile based on ION protocol.

 

Please use the "Set Up Project" tab on the Profil Editor.

 

Romain_Polette_0-1744637609680.png

 

Do not forget to export your project before exiting Profile Editor.

 

Once PM8000 profile added to your project, you can create a PM8000 I/O Device thanks to the I/O Device Manager.

Romain_Polette_1-1744637918345.png

 

Regards, 

 

 

Romain POLETTE
Solution Architect - France Operations
Reply
YunusArat
Lieutenant | EcoXpert Master YunusArat Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2025-04-16 12:40 AM

0 Likes
0
142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-16 12:40 AM

1) I tryed your solved. I can read the device from ethernet port. I see the document max device is 8. I have a lat of device. Is there any problem here?

 

2) I want to read th device from serial port with pas600L (schneider eth gateway). But I cat read. You can see the my settings. I try port 502 and 7700. not solved.  

 

 

 

 

 

YunusArat_0-1744789305181.jpeg

 

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2025-04-16 06:42 AM

1 Like
0
131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-04-16 06:42 AM

Hello @YunusArat , 

Panel Server is not compatible with ION Protocol.
PM8000 connected through Modbus Serial is native to PAS600 and PAS800. Please check at least your PM8000 COM1 parameters are aligned with the Serial parameters of the Panel Server (8E1 by default). At this level you must be able to read PM8000 Modbus Registers through the "Register Read" feature of the Panel Server.

 

EcoStruxure Power Operation has no Modbus Device Profile for PM8000. You have to create one based on the PM8000 Modbus Map and EPO PwrModbus driver.

For better integration, it is strongly recommended to connect your PM8000 to EPO through ION Ethernet.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of