Hi @YunusArat ,
PM8000 is native to Power Operation.
There is a default PM8000 Device Profile based on ION protocol.
Please use the "Set Up Project" tab on the Profil Editor.
Do not forget to export your project before exiting Profile Editor.
Once PM8000 profile added to your project, you can create a PM8000 I/O Device thanks to the I/O Device Manager.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @YunusArat ,
Panel Server is not compatible with ION Protocol.
PM8000 connected through Modbus Serial is native to PAS600 and PAS800. Please check at least your PM8000 COM1 parameters are aligned with the Serial parameters of the Panel Server (8E1 by default). At this level you must be able to read PM8000 Modbus Registers through the "Register Read" feature of the Panel Server.
EcoStruxure Power Operation has no Modbus Device Profile for PM8000. You have to create one based on the PM8000 Modbus Map and EPO PwrModbus driver.
For better integration, it is strongly recommended to connect your PM8000 to EPO through ION Ethernet.
Regards,
Link copied. Please paste this link to share this article on your social media post.
There is already a device profile under "Create Device Profiles" called "PM8000 Standard". It uses the ION device type like the other ION meters.
In the future, you may want to post these types of questions on the EcoStruxure Power Operation board.
Link copied. Please paste this link to share this article on your social media post.
Hi @YunusArat ,
PM8000 is native to Power Operation.
There is a default PM8000 Device Profile based on ION protocol.
Please use the "Set Up Project" tab on the Profil Editor.
Do not forget to export your project before exiting Profile Editor.
Once PM8000 profile added to your project, you can create a PM8000 I/O Device thanks to the I/O Device Manager.
Regards,
Link copied. Please paste this link to share this article on your social media post.
1) I tryed your solved. I can read the device from ethernet port. I see the document max device is 8. I have a lat of device. Is there any problem here?
2) I want to read th device from serial port with pas600L (schneider eth gateway). But I cat read. You can see the my settings. I try port 502 and 7700. not solved.
Link copied. Please paste this link to share this article on your social media post.
Hello @YunusArat ,
Panel Server is not compatible with ION Protocol.
PM8000 connected through Modbus Serial is native to PAS600 and PAS800. Please check at least your PM8000 COM1 parameters are aligned with the Serial parameters of the Panel Server (8E1 by default). At this level you must be able to read PM8000 Modbus Registers through the "Register Read" feature of the Panel Server.
EcoStruxure Power Operation has no Modbus Device Profile for PM8000. You have to create one based on the PM8000 Modbus Map and EPO PwrModbus driver.
For better integration, it is strongly recommended to connect your PM8000 to EPO through ION Ethernet.
Regards,