Good day,
Hope you are well.
Is it possible use the input on a VL12 can be set to switch off the system when the site is running on a generator.
I have check on the user guide. I saw these below, not sure if can be used to turn off all the capacitors.
“Switching on Cos φ2 via Digital Input
or P Export
If a dry contact is connected to the digital input terminal, the controller will
switch to Cos φ2 and display "NT."
• Connected output dry contact between terminal I1, I2. Voltage source
internally supplied: 5 V DC - 10 mA. Recommended section ≥ 1 mm².
Length of cable should be less than 100 m.
• Set item 510 in advanced menu:
- Yes = digital input is activated with closed terminals I1 & I2
- No = digital input is activated with open terminals I1 & I2.
• Set Cos φ2 target in 303.
Also, the controller is able to switch to Cos φ2 when P EXPORT is detected
(from load to grid)
• Set item 504:
- Yes = the controller operates in P-export with the Cos φ2 as control target.
- No = the controller operates in P-export with the Cos φ1.”
Link copied. Please paste this link to share this article on your social media post.
Yes, when operating on the generator on site, the digital input on VL12 can be used to switch to "Cos φ 2" to turn off all capacitors. Cos φ 2 can be set very low, so there is no need to open all capacitors.
If a dry contact is connected to the digital input terminal, the controller will
switch to Cos φ2 and display "NT."
• Connected output dry contact between terminal I1, I2. Voltage source
internally supplied: 5 V DC - 10 mA. Recommended section ≥ 1 mm².
Length of cable should be less than 100 m.
• Set item 510 in advanced menu:
- Yes = digital input is activated with closed terminals I1 & I2
- No = digital input is activated with open terminals I1 & I2.
• Set Cos φ2 target in 303.
Also, the controller is able to switch to Cos φ2 when P EXPORT is detected
(from load to grid)
• Set item 504:
- Yes = the controller operates in P-export with the Cos φ2 as control target.
- No = the controller operates in P-export with the Cos φ1.”
Link copied. Please paste this link to share this article on your social media post.
Yes, when operating on the generator on site, the digital input on VL12 can be used to switch to "Cos φ 2" to turn off all capacitors. Cos φ 2 can be set very low, so there is no need to open all capacitors.
If a dry contact is connected to the digital input terminal, the controller will
switch to Cos φ2 and display "NT."
• Connected output dry contact between terminal I1, I2. Voltage source
internally supplied: 5 V DC - 10 mA. Recommended section ≥ 1 mm².
Length of cable should be less than 100 m.
• Set item 510 in advanced menu:
- Yes = digital input is activated with closed terminals I1 & I2
- No = digital input is activated with open terminals I1 & I2.
• Set Cos φ2 target in 303.
Also, the controller is able to switch to Cos φ2 when P EXPORT is detected
(from load to grid)
• Set item 504:
- Yes = the controller operates in P-export with the Cos φ2 as control target.
- No = the controller operates in P-export with the Cos φ1.”
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of