Good day,
Hope you are well.
Is it possible use the input on a VL12 can be set to switch off the system when the site is running on a generator.
I have check on the user guide. I saw these below, not sure if can be used to turn off all the capacitors.
“Switching on Cos φ2 via Digital Input
or P Export
If a dry contact is connected to the digital input terminal, the controller will
switch to Cos φ2 and display "NT."
• Connected output dry contact between terminal I1, I2. Voltage source
internally supplied: 5 V DC - 10 mA. Recommended section ≥ 1 mm².
Length of cable should be less than 100 m.
• Set item 510 in advanced menu:
- Yes = digital input is activated with closed terminals I1 & I2
- No = digital input is activated with open terminals I1 & I2.
• Set Cos φ2 target in 303.
Also, the controller is able to switch to Cos φ2 when P EXPORT is detected
(from load to grid)
• Set item 504:
- Yes = the controller operates in P-export with the Cos φ2 as control target.
- No = the controller operates in P-export with the Cos φ1.”
Yes, when operating on the generator on site, the digital input on VL12 can be used to switch to "Cos φ 2" to turn off all capacitors. Cos φ 2 can be set very low, so there is no need to open all capacitors.
(from load to grid)
• Set item 504:
(from load to grid)