Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
michael_franz
michael_franz
Mentor
Posted: ‎2017-08-02 06:47 AM
2
1448
iem3555 Phase A odd
TEAM:
Here is a screen capture of what we are reading for one of the iem3555 meters at a site.
Note that current A is a significantly higher than B or C ampere readings and the kW is negative.
Does anyone have a guess on why this would be?  All that I can come up with is either a bad sensor, the wrong sensor type on that phase or a problem with the meter itself.
Has anyone else witnessed this issue?
Sincerely,
Michael Franz l APC
Technical Consultant
Tags (4)
  • current sensor
  • iem3000
  • iem3555
  • phase a
Yut
Yut
Leader
Posted: ‎2017-08-02 11:25 PM
1
1424
Check wiring.
michael_franz
michael_franz
Mentor
Posted: ‎2017-08-03 05:35 AM
Yut:
Our electricians have checked the wiring.  I would suspect that if "A” were
backwards then it would read close to the rest in a balanced system but be
negative.
Here we are negative and over 40 times different than the other phases.
We believe that it is a malfunctioning sensor that is causing the issue.
Sincerely,
Michael