What might be the possible causes when meters cannot sense low current
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2013-11-1509:43 AM
This very much device specific and a function of the dynamic range of the device. It depends on front end analogue design, A/D convertor used and of course firmware/software.
It is common in firmware to consider sampled readings below a certain threshold to be noise and set the reading to zero. While there maybe engineering and test data which has this information it is often not publish in the public specification.
If a CT has been chosen that has to large a primary rating then on the secondary side at the lower end there is not enough current to get a reading. For example if the CT was 10000:5 but the actual bus current was only 10A then the current signal at the device would be 5mA and that might be to low for the device to read.
Finally I seen installations where on the metering terminal block the CT shorting mechanism (required for safety and maintenance) has been left in place. This of course means little or no current at the device.