Hi I'm looking for a solution to measure the non-integer harmonics.
Thanks
Posted: 2013-11-12 12:12 PM
Link copied. Please paste this link to share this article on your social media post.
Hi Abon Chen, I suppose you are talking about inter-harmonics, if so you will need an ION7650 or ION8650A.
Posted: 2013-11-12 06:58 PM
Link copied. Please paste this link to share this article on your social media post.
What is the resolution for 7650 and 8650?
I would like to have 1/10 resolution.
For example, 1.1 1.2 1.3 1.4 multiple
Of fundamental frequency.
Thanks
Sent from mobile
"Mauro Carrenho" <powersolutionscommunity-admin@powersolutionscommunity.hosted.jivesoftware.com> 於 2013/11/13 3:57 寫道:
Solutions Expert Community
Do we have meter that can measure non integer harmonics?
reply from Mauro Carrenho in Power Monitoring Hardware - View the full discussion
Hi Abon Chen, I suppose you are talking about inter-harmonics, if so you will need an ION7650 or ION8650A.
Reply to this message by replying to this email, or go to the message on Solutions Expert Community
Start a new discussion in Power Monitoring Hardware by email or at Solutions Expert Community
Following Do we have meter that can measure non integer harmonics? in these streams: Inbox
>
Posted: 2013-11-13 05:42 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Abon Chen, I am not an expert on Power Quality but as far as I understand usually when we talk about interharmonics we don't specify the exactly frequency like in your example, we just have the entire interharmonic band between 2 integers harmonics... But maybe an expert can be more clear in the explanation and also give you more details.
Please find below part of the Harmonic measurement Module from the ION Reference, detailing how this module works.
Magnitude
These 50 output registers provide the magnitude of each harmonic or interharmonic.
When the module is operating in inter‐harmonics mode, magnitude
identifies the signal component between the (n‐1) and (nth) harmonic; for example,
Magnitude 2 specifies the inter‐harmonic band between the fundamental and
the 2 nd harmonic.
The module performs harmonic analysis using the method outlined in the
standard IEC 61000‐4‐7 Harmonic and interharmonics Class I and II. The
frequency resolution is 5 Hz.
Posted: 2013-11-13 06:03 AM
Link copied. Please paste this link to share this article on your social media post.
Thanks for referring to the ION module. Based on the description, it seems that I can only specify inter-harmonic measurement between the adjacent harmonics I specified.
Posted: 2013-11-18 11:40 PM
Link copied. Please paste this link to share this article on your social media post.
To measure all the interharmonics within 50th harmonics , I am thinking about setting n from 1 to 50 for every 5 minutes. So I can get a full range measurements in every 250minutes.
To change ION7650 configuration dynamically, what is the best tool to implement?