What includes the BCPMSCA60S reference

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
YvesR
Ensign Ensign
Ensign
0 Likes
1
243

What includes the BCPMSCA60S reference

Hello,

I want to quote a BCPM split core

when order the BCPMSCA60S reference is included;

main unit

board for CT connection

cable between main unit and board (round or flat)

and 60 50A CT's?

Thanks in advance?

Yves


Accepted Solutions
Adam_Hardman
Commander Commander
Commander
0 Likes
0
224

Re: What includes the BCPMSCA60S reference

Models with more than 2 as the number of circuits include 50 A branch CTs with 2 meter leads and 1.8M round ribbon cables.

The BCPMSC models with 1, 2 or Y63 as the number of circuits DO NOT INCLUDE ANY branch CTs or ribbon cables (they include only the Main board and adapater board assemblies) . These models are provided to allow users to order a

specific combination of CT quantities, CT sizes, CT lead lengths and ribbon cable styles and lengths.

The CTs and cables must be ordered separately.

The PowerLogic BCPMSC uses .333 V AC output split-core CTs for the auxiliary inputs. These CTs are ordered separately from the BCPM.

See Answer In Context

1 Reply 1
Adam_Hardman
Commander Commander
Commander
0 Likes
0
225

Re: What includes the BCPMSCA60S reference

Models with more than 2 as the number of circuits include 50 A branch CTs with 2 meter leads and 1.8M round ribbon cables.

The BCPMSC models with 1, 2 or Y63 as the number of circuits DO NOT INCLUDE ANY branch CTs or ribbon cables (they include only the Main board and adapater board assemblies) . These models are provided to allow users to order a

specific combination of CT quantities, CT sizes, CT lead lengths and ribbon cable styles and lengths.

The CTs and cables must be ordered separately.

The PowerLogic BCPMSC uses .333 V AC output split-core CTs for the auxiliary inputs. These CTs are ordered separately from the BCPM.