Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

Synchronizing ION 92040 via IRIG-B

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Synchronizing ION 92040 via IRIG-B
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
292
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
71
Robert_Lee
Captain Robert_Lee Captain
67
View All
Related Products
product field
Schneider Electric
PowerLogic ION9000

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
ManuelTrebilcock
Lieutenant JG ManuelTrebilcock Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-21 09:10 AM

0 Likes
2
941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-21 09:10 AM

Synchronizing ION 92040 via IRIG-B

Hello everyone,

 

We are in the design phase of an architecture intended to synchronize 6 ION 92040 via IRIG-B. The time server must be a GE RT430.

In the ION manual is stated that you can connect an IRIG-B source to one of the meter's digital input for IRIG-B synchronization and that you must configure both, the meter's digital input and the meter's clock. I have the following questions: 

  • What's the configuration you have to do?
  • Which technique can be used to transmit the unmodulated code, TTL, RS232, RS485, etc, and how to connect it to the digital input properly?
  • Can you implement a daisy chain connection for the synchronization of all the meters?

 

Beforehand, thank you for your time.

 

 

Best regards,

 

Manuel Trebilcock

  • Thumbnail of PowerLogic ION9000
    Schneider Electric
    PowerLogic ION9000
View products (1)
Labels
  • Labels:
  • ION9000
Tags (3)
  • Tags:
  • english
  • ion9000
  • IRIG-B
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Yut
Captain Yut
Captain

Posted: ‎2021-11-06 04:58 PM

0 Likes
0
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-06 04:58 PM

I'm working with the GPS Synchronize for long time. ION meter can do time synchronize as follow.

To serial port, the clock transmits signal in ASCII format such as Truetime/Datum meters can be daisy chain connected via RS-485 fashion network .

To IRIG-B port (On board DI), clock transmits signal in TTL, DCLS whatever the manufacturer of the clock called unmodulated type this can be daisy chain as long as the the total impedance do exceed the clock output capability i.e. 10k ohms in case of the Arbiter brand.

 

For service

If ASCII type, a computer install with Hyper Terminal software or any is needed for monitor the signal.

IF IRIG-B type, an oscilloscope is needed for monitor the signal.

 

Time sync. check can be done using diagnostics module output monitor see ION Reference. 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-10-21 04:57 PM

1 Like
1
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-21 04:57 PM

Hello @ManuelTrebilcock 

 

For the configurations, there are 2 modules I know of that need to be configured. The clock module's time synchronization source and Digital input's mode needs to be set to IRIG-B

 

 

@DanL 

Do you know the answers to the questions:

  • Which technique can be used to transmit the unmodulated code, TTL, RS232, RS485, etc, and how to connect it to the digital input properly?
  • Can you implement a daisy chain connection for the synchronization of all the meters?

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Yut
Captain Yut
Captain

Posted: ‎2021-11-06 04:58 PM

0 Likes
0
873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-06 04:58 PM

I'm working with the GPS Synchronize for long time. ION meter can do time synchronize as follow.

To serial port, the clock transmits signal in ASCII format such as Truetime/Datum meters can be daisy chain connected via RS-485 fashion network .

To IRIG-B port (On board DI), clock transmits signal in TTL, DCLS whatever the manufacturer of the clock called unmodulated type this can be daisy chain as long as the the total impedance do exceed the clock output capability i.e. 10k ohms in case of the Arbiter brand.

 

For service

If ASCII type, a computer install with Hyper Terminal software or any is needed for monitor the signal.

IF IRIG-B type, an oscilloscope is needed for monitor the signal.

 

Time sync. check can be done using diagnostics module output monitor see ION Reference. 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc