Hello,
I got an enquiry from a client to provide a retrofit solution on existing panels which have no existing power meters. My client wants a solution with split core CT to minimize the downtime.
I had a look at some split core CT such as PowerLogic Split Core Current Transformers.
There are 3 x 4 pole ACBs at site and each phase has from 2 to 4 power cables. As these CTs are described to be used for busbars, can they also be used for power cables as shown in the attached picture ?
Please let me know.
Thanks in advance.
Existing Cables.jpg
Link copied. Please paste this link to share this article on your social media post.
Yes, you can.
You also could use rogowski with a transducer. Realy easy!
Have used this several times with good experience;
https://www.phoenixcontact.com/en-no/products/current-transformer-pact-rcp-4000a-1a-d140-2904922
BR
GIA
Link copied. Please paste this link to share this article on your social media post.
Yes, you can.
You also could use rogowski with a transducer. Realy easy!
Have used this several times with good experience;
https://www.phoenixcontact.com/en-no/products/current-transformer-pact-rcp-4000a-1a-d140-2904922
BR
GIA