SERIAL CONNECTION BETWEEN PM5100 series and A9MEM3150

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • SERIAL CONNECTION BETWEEN PM5100 series and A9MEM3150
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
484
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Anonymous user
Not applicable

Posted: ‎2021-03-26 12:40 AM

0 Likes
3
1439
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-26 12:40 AM

SERIAL CONNECTION BETWEEN PM5100 series and A9MEM3150

Dears All,

Can I make serial connection between PM5100 series and A9MEM3150?

If it is possible, what are the max. quantity?

 

Thank you so much for your support.

 

B&R

Ayşegül

 

Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-03-26 11:17 AM

1 Like
2
1434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-26 11:17 AM

Hello @Anonymous user ,

 

Both meters support Modbus RTU over RS-485 link. Both support the same baud rates and same parity (even odd none). The question about how many can be connected is an ambiguous question. A lot depends on how the devices will be used. 

 

A system with devices being polled once every 15 minutes with an acceptable delay of 15 seconds could support a lot more devices than a system polling devices every 5 seconds with 3 second delay maximum. (Assuming both devices support polling this fast).

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2021-03-28 11:33 AM

0 Likes
1
1423
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-28 11:33 AM

Dear Charles,

Thank you so much for your support.

 

5 units PM5100 and 1 unit A9MEM31. I think it is possible to make serial conection between them. What are the maximum quantity?

 

B&R

Ayşegül

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-03-29 01:00 PM

0 Likes
0
1415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-29 01:00 PM

Hello @Anonymous user ,

 

Again the maximum quantity is not an answer I can give because there are different factors. There are limits based on distances between devices for different baud rates. There are limited based on how much traffic is expected on the serial line. There are limits based on the modbus protocol itself. Then there is also limits based on what the gateway (or Modbus Master device) can handle in turns of burden. All of these factors and others come together to make a limit based on what is needed from the system.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of