SERIAL CONNECTION BETWEEN PM5100 series and A9MEM3150

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

AYSEGUL
Ensign Ensign
Ensign
0 Likes
3
738

SERIAL CONNECTION BETWEEN PM5100 series and A9MEM3150

Dears All,

Can I make serial connection between PM5100 series and A9MEM3150?

If it is possible, what are the max. quantity?

 

Thank you so much for your support.

 

B&R

Ayşegül

 

Tags (1)
3 Replies 3
Charles_Murison
Picard Picard
Picard

Re: SERIAL CONNECTION BETWEEN PM5100 series and A9MEM3150

Hello @AYSEGUL ,

 

Both meters support Modbus RTU over RS-485 link. Both support the same baud rates and same parity (even odd none). The question about how many can be connected is an ambiguous question. A lot depends on how the devices will be used. 

 

A system with devices being polled once every 15 minutes with an acceptable delay of 15 seconds could support a lot more devices than a system polling devices every 5 seconds with 3 second delay maximum. (Assuming both devices support polling this fast).

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
AYSEGUL
Ensign Ensign
Ensign
0 Likes
1
722

Re: SERIAL CONNECTION BETWEEN PM5100 series and A9MEM3150

Dear Charles,

Thank you so much for your support.

 

5 units PM5100 and 1 unit A9MEM31. I think it is possible to make serial conection between them. What are the maximum quantity?

 

B&R

Ayşegül

 

Tags (1)
Charles_Murison
Picard Picard
Picard
0 Likes
0
714

Re: SERIAL CONNECTION BETWEEN PM5100 series and A9MEM3150

Hello @AYSEGUL ,

 

Again the maximum quantity is not an answer I can give because there are different factors. There are limits based on distances between devices for different baud rates. There are limited based on how much traffic is expected on the serial line. There are limits based on the modbus protocol itself. Then there is also limits based on what the gateway (or Modbus Master device) can handle in turns of burden. All of these factors and others come together to make a limit based on what is needed from the system.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)