Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Rogowski Coils

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Rogowski Coils
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
richard_schwass
richard_schwass
Explorer

Posted: ‎2016-06-12 09:41 PM

0 Likes
10
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-12 09:41 PM

Rogowski Coils

Hi there,

Do any of the metering offer work with Rogowski Coils?

If not (as I suspect) are the intermediate devices that might be able to interface these to a current input?

What about the 0-1volt option "F" on the ION7650 - would this work?

Regards Richard

Tags (1)
  • Tags:
  • rogowski coils
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Yut
Yut
Leader

Posted: ‎2016-06-14 01:42 AM

0 Likes
5
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-14 01:42 AM

ION7650 NICT is fine you can use 1V or .333V output. See www.magnelab.com.

See Answer In Context

Reply
Replies 10
sesa63638
sesa63638 Explorer
Explorer

Posted: ‎2016-06-13 12:24 AM

1 Like
1
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-13 12:24 AM

Richard,

in advanced energy metering there are 2 solutions with our Rogowski U018 coils

a) Enercept EM4200 serie

b) iEM3500 series (A9MEM3555 or A9MEM3565)

Reply
Yut
Yut
Leader

Posted: ‎2016-06-14 01:42 AM

0 Likes
5
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-14 01:42 AM

ION7650 NICT is fine you can use 1V or .333V output. See www.magnelab.com.

Reply
richard_schwass
richard_schwass
Explorer

Posted: ‎2016-06-14 01:56 AM

0 Likes
2
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-14 01:56 AM

Hi Yut

Thanks for your comment. Do the meters allow for the phase shift of the rope ct's in the firmware?

Also is 1v or 0.333v best if you had a choice? And is it an AC or DC voltage?

Trust things are well in Thailand

Regards Richard

Reply
Anonymous user
Not applicable

Posted: ‎2016-06-14 07:11 AM

0 Likes
1
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-14 07:11 AM

Hi Richard,

The EM4300 series energy meters are equipped with 3 permanently attached Rogowski coils, and communicate with the Com'X 200/210, Com'X 510 or SSL MPM gateway devices via ZigBee.

You can search "EM4300 series on the Schneider website for more information. Search - Schneider Electric

Best regards,

Cesar

Reply
Yut
Yut
Leader

Posted: ‎2016-06-14 10:37 PM

0 Likes
1
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-14 10:37 PM

Richard, output is AC you can set phase shift using telnet command. I cannot tell what is best it depends on the CT design.

Reply
richard_schwass
richard_schwass
Explorer

Posted: ‎2016-06-15 04:39 PM

0 Likes
0
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-15 04:39 PM

Thanks for your input Patrick

Reply
richard_schwass
richard_schwass
Explorer

Posted: ‎2016-06-15 04:39 PM

0 Likes
0
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-15 04:39 PM

Really appreciate you advice Yut, Thank you.

Reply
richard_schwass
richard_schwass
Explorer

Posted: ‎2016-06-15 04:40 PM

0 Likes
0
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-06-15 04:40 PM

Understood, thanks Cesar

Reply
engenharia_memt
engenharia_memt
Explorer

Posted: ‎2017-11-06 12:12 PM

0 Likes
1
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-11-06 12:12 PM

hello Yut,

have you already used this rugowsky coils from magnelab?

i´m looking some information from their web site and seems very nice product.

i have only one point that i need to clear is regarding the starting current with good amplitude and frequency responses.

have you some measurement tests of harmonics results to share with us?

Reply
Yut
Yut
Leader

Posted: ‎2017-11-06 07:50 PM

0 Likes
0
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-11-06 07:50 PM

I recommend  the blue one from Universal Technic it performs very well except when current is overload it saturated. We test the Magnelab briefly just to show to customer who own it.

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore