Reset counters through Modbus in metsepm5330
Metering & Power Quality
Select a Country
  • EcoStruxure Power & Grid
  • Reset counters through Modbus in metsepm5330
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
195
Ramasamy_N
Ramasamy_N Champion
115
PowerLogic PM5000 series
MauroDiam
MauroDiam
Explorer
Posted: ‎2023-12-23 01:20 PM
1218
Hello, is there a way to reset energy counter and max/min values through Modbus?
I searched the registers to do that in the modbus registers map , but I wasn't able to find them.
  • Thumbnail of PowerLogic PM5000 series
View products (1)
  • PM5000
Mehran_Mehrnia
Champion
Posted: ‎2024-01-04 04:19 PM
Hi @MauroDiam
For PM5000 series, in order to send command through Modbus to perform registers reset like Min/Max values, please follow the steps in the following FAQ:
Procedure to send commands over Modbus to PM5000 using Modbus Tester
https://www.se.com/eg/en/faqs/FA241856/
- Read Command Semaphore value which is stored in Modbus register 5680(only perform the reading operation once or in the next 4 minutes)
- Set register Requested Command 5000 to the Command value 2009(Reset All Min/Max)
- Set register Command Semaphore 5001 to the Semaphore value retrieved in first step
- Then click on 'Write' button
Best Regards,
-Mehran
Expert Technical Support Specialist
Mehran_Mehrnia
Champion
Hi @MauroDiam
Best Regards,
-Mehran