Regarding meter side during withstand voltage test

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Regarding meter side during withstand voltage test
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
522
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
136
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Miyai
Lieutenant Miyai
Lieutenant

Posted: ‎2025-10-29 10:12 PM

0 Likes
3
248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-29 10:12 PM

Regarding meter side during withstand voltage test

Hello,


I'd like some advice on what to do when testing meter.

 

When performing a withstand voltage test or insulation resistance test after installing an ION9000, PM8000, or PM5000 on a panel, how do you handle voltage measurement circuit and control power supply circuit?

 

Also, how does the ION9000 handle ground wiring?
Do I need to disconnect ground wire from terminal?


Generally, if it is not possible to perform a withstand voltage test or the like, there will be a note in the manual.
However, I was unable to find any mention of this in the manual for the meter mentioned above.

 

Therefore, I would like some advice on wiring connections during testing.

 

Best regards,

Miyai

Labels
  • Labels:
  • ION9000
  • PM5000
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
Admiral

Posted: ‎2025-10-30 08:30 AM

0 Likes
0
233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-30 08:30 AM

Hi @Miyai 

 

All ION meters are subjected to hi-pot testing during the manufacturing process, ensuring their dielectric integrity before deployment. As a result, repeating such tests in the field is not only unnecessary but can be harmful.

 

After factory testing, additional surge protection circuitry, typically consisting of MOVs, fuses, etc., is integrated into the meter to shield it from transient over voltages caused by lightning or upstream electrical disturbances.

 

While this protection enhances the meter’s resilience to real-world surge events, it also makes the meter vulnerable to damage if subjected to dielectric withstand voltage tests without first disconnecting these circuits and components. Therefore, performing hi-pot tests in the field without isolating the surge protection circuitry can inadvertently trigger or destroy these components, leading to meter failure.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-10-30 02:15 PM

0 Likes
1
219
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-30 02:15 PM

Hello @Miyai ,

 

While the ION9000 and PM8000 meters do not mention Hi-pot specific, there is a comment under Safety precautions. "Do not exceed the maximum ratings of this device."  safety-precautions 

As Mehran has said the meter has protection devices that will save internal electronics however will cause the meter to no longer be operable.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 3
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
Admiral

Posted: ‎2025-10-30 08:30 AM

0 Likes
0
234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-30 08:30 AM

Hi @Miyai 

 

All ION meters are subjected to hi-pot testing during the manufacturing process, ensuring their dielectric integrity before deployment. As a result, repeating such tests in the field is not only unnecessary but can be harmful.

 

After factory testing, additional surge protection circuitry, typically consisting of MOVs, fuses, etc., is integrated into the meter to shield it from transient over voltages caused by lightning or upstream electrical disturbances.

 

While this protection enhances the meter’s resilience to real-world surge events, it also makes the meter vulnerable to damage if subjected to dielectric withstand voltage tests without first disconnecting these circuits and components. Therefore, performing hi-pot tests in the field without isolating the surge protection circuitry can inadvertently trigger or destroy these components, leading to meter failure.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-10-30 02:15 PM

0 Likes
1
220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-30 02:15 PM

Hello @Miyai ,

 

While the ION9000 and PM8000 meters do not mention Hi-pot specific, there is a comment under Safety precautions. "Do not exceed the maximum ratings of this device."  safety-precautions 

As Mehran has said the meter has protection devices that will save internal electronics however will cause the meter to no longer be operable.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Miyai
Lieutenant Miyai
Lieutenant

Posted: ‎2025-11-04 09:00 PM

0 Likes
0
175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-04 09:00 PM

Hello @Charles_Murison , @Mehran_Mehrnia 

 

Thank you for advice.
I will exclude the meter from the voltage withstand test.

 

 

Best regards,

Miyai

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore