Hi
According to User Manual PHA6516400-05 page 16 it states that the baud rate can be set to higher value than 9600 (38400/19200).
If so really good then using this meter together with other =S= meters and Panel Server that has baud rate 19200 as standard setting.
Baud rate 9600 is stated in earlier versions of the User Manual and also in the hardware was this the highest baud rate possible to set.
Has there been an hardware upgrade and if so from what date code ?
Wrong in User Manual ?
BR/Anders
PAE EcoStruxure Power, Sweden
Link copied. Please paste this link to share this article on your social media post.
Hi @AndersDahlskog,
I'm sorry for the delay; I was gathering the information.
There were some hardware changes in the iEM2050 and iEM2055 to support higher baud rates. For the iEM2050, the start date is 17 June 2024, and for the iEM2055, it is 29 July 2024.
Best Regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Hi @AndersDahlskog,
I'm sorry for the delay; I was gathering the information.
There were some hardware changes in the iEM2050 and iEM2055 to support higher baud rates. For the iEM2050, the start date is 17 June 2024, and for the iEM2055, it is 29 July 2024.
Best Regards,
JD