Range of the power factor register (Modbus Register number 3150, Power Factor Total) of ION9000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Range of the power factor register (Modbus Register number 3150, Power Factor Total) of ION9000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Tomohiro-Okada
Lieutenant JG Tomohiro-Okada
Lieutenant JG

Posted: ‎2022-04-08 03:44 AM

0 Likes
4
2442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-08 03:44 AM

Range of the power factor register (Modbus Register number 3150, Power Factor Total) of ION9000

Hello,

 

I have two question about power factor register(Modbus Register number 3150, Power Factor Total) of ION9000.

 

I think the relation between the display value of power factor and the internal register value is below.

Display Value:0.0000LG~1.0000LG ⇒ Register Value: 0.0000 ~ -1.0000

Display Value:0.0000LD~1.0000LD ⇒ Register Value:0.0000 ~ +1.0000

(Finally, the range of the register is -1.0000 ~ 0.000 ~ 1.0000)

 

Is my understanding correct?

 

Another question is that if the display value is 0.0000LG, the register value can be like -0.0000?

(the register value is expressed by adding sign to zero?)

I'd like to know how to distinguish Lag or Lead by using register value (3150 Power Factor) when the value is zero?

 

Thanks,

@Tomohiro-Okada 

 

 

 

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2022-04-08 10:00 AM

0 Likes
3
2420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-08 10:00 AM

The ION9000 supports two different methods for presenting a sign for power factor via the "PF Sign Convention" setup register in the Power Meter Module.

https://www.productinfo.schneider-electric.com/ion9000/595e26f146e0fb0001f6ffc4/IONReference/English...

 

The supported sign conventions for the signed PF outputs are:

1. "IEEE": The sign encodes Lead vs Lag. Quadrants 2 & 4 (Lead) are positive. Quadrants 1 & 3 (Lag) are negative.

2. "IEC": The sign encodes the direction of flow of active power. Quadrants 1 & 4 (delivered) are positive. Quadrants 2 & 3 (received) are negative.

 

When the PF Lead registers are > 0.0, the PF is Leading
When the PF Lag registers are > 0.0, the PF is Lagging

See Answer In Context

Attachments
Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2022-04-11 02:23 PM

0 Likes
1
2358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-11 02:23 PM

Register 3150 is computed as:
PFtot = Ptot / Stot * signConvention

where Ptot = (signed) total active power and Stot = (unsigned) total apparent power

NOTE: ION meters support two definitions of total apparent power. Please ensure the meter is configured to use the appropriate definition. Utilities tend to prefer "Vector Sum". Demand customers often prefer "Scalar Sum".

 

while using the IEEE setting, signConvention = -sign(Q)

where Q = reactive power

 

values that end up exactly on a boundary between quadrants are technically neither lagging nor leading (ie. -1, +1, -0, +0)

A values of -1.000000 and -0.000000 are much more likely when there is a nonlinear load (causing distortion) and you are using the default "Vector Sum" method for kVA_total.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 4
DanL
Captain DanL Captain
Captain

Posted: ‎2022-04-08 10:00 AM

0 Likes
3
2421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-08 10:00 AM

The ION9000 supports two different methods for presenting a sign for power factor via the "PF Sign Convention" setup register in the Power Meter Module.

https://www.productinfo.schneider-electric.com/ion9000/595e26f146e0fb0001f6ffc4/IONReference/English...

 

The supported sign conventions for the signed PF outputs are:

1. "IEEE": The sign encodes Lead vs Lag. Quadrants 2 & 4 (Lead) are positive. Quadrants 1 & 3 (Lag) are negative.

2. "IEC": The sign encodes the direction of flow of active power. Quadrants 1 & 4 (delivered) are positive. Quadrants 2 & 3 (received) are negative.

 

When the PF Lead registers are > 0.0, the PF is Leading
When the PF Lag registers are > 0.0, the PF is Lagging

Attachments
Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant JG Tomohiro-Okada
Lieutenant JG

Posted: ‎2022-04-09 02:50 AM

0 Likes
2
2401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-09 02:50 AM

Hello @DanL 

 

Thank you for your reply.

 

I understand relation between Quadrants and register value(Modbus Register 3150) .

(The relation between them is changed when the meter setting is "IEEE" or "IEC")

 

Then, can the Modbus Register  value be following numbers?(when the meter setting is IEEE)

 

・ -1.0000 (I think the value means same with 1.000)

・ -0.0000 (If the register can be the value, I think it means power factor is zero and lagging)

 

I was asked  by my customer to tell them available  value  of the register( Modbus Register 3150).

 

Regards,

@Tomohiro-Okada 

 

 

 

Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2022-04-11 02:23 PM

0 Likes
1
2359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-11 02:23 PM

Register 3150 is computed as:
PFtot = Ptot / Stot * signConvention

where Ptot = (signed) total active power and Stot = (unsigned) total apparent power

NOTE: ION meters support two definitions of total apparent power. Please ensure the meter is configured to use the appropriate definition. Utilities tend to prefer "Vector Sum". Demand customers often prefer "Scalar Sum".

 

while using the IEEE setting, signConvention = -sign(Q)

where Q = reactive power

 

values that end up exactly on a boundary between quadrants are technically neither lagging nor leading (ie. -1, +1, -0, +0)

A values of -1.000000 and -0.000000 are much more likely when there is a nonlinear load (causing distortion) and you are using the default "Vector Sum" method for kVA_total.

Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant JG Tomohiro-Okada
Lieutenant JG

Posted: ‎2022-04-14 12:04 AM

0 Likes
0
2323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-04-14 12:04 AM

Hi @DanL,

 

Thank you for your prompt reply.

I understand about this.

 

Thanks,

Okada

 

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of