Hello - I am trying to figure-out how to calculate the register numbers for:HDPM6000. for the branch circuits on the HDPM6000:
- I_Avg
- V_Avg
- PF_tot
- kVAR_total
- kW Real
The HDPM has 42 branches and configured for 14 3-phase circuits. The circuits are grouped like:
Ckt Channels
A 1,3,5
B 2,4,6
C 7,9,11
D 8,10,12
etc......
I had looked at the protocol guide and can't quite figure this out.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Hello @Anonymous user
I am assuming you are referring to https://www.se.com/ww/en/download/document/ZL0192-0A/ as protocol guide.
Looking at page 1 I see the following information:
"For simplicity, this document only deals with Modbus addresses using 0-based numbering. Modbus terminology puts register 1 is at address 0."
Per Circuit Registers
C = (channel number * 10) – where the channel number ranges from 1 to 192.
Register Value
C + 0 VRMS in 0.1V steps (other steps maybe configured in regs 4498-4501)
C + 1 Circuit number (for creating single, two, three or four phase circuits)
C + 2 IRMS in 10mA steps (other steps maybe configured in regs 4498-4501)
C + 3 CT Type
C + 4 Pfactor * 1000 (signed)
C + 5 Watts in 1W steps (other steps maybe configured in regs 4498-4501)
C + 6 CT Factor * 1000
C + 7 iTHD
C + 8 Phase (1, 2 or 3) - 0 is disconnected
C + 9 Expected phase (1, 2 or 3) – as programmed during setup
Examples:
• VRMS for circuit 1 would be address 10 (1 * 10) + 0
• Power factor for circuit 9 would be address 94 (9 * 10) + 4
C + 1 Circuit number
This number is used to indicate whether channels should be grouped together
as two phase or three phase circuits – or left as a single phase circuit.
Examples:
• Channels that have a unique circuit number will be treated as single
phase circuits.
• If channels 3 and 5 have the same circuit number, e.g. 3, these will be
treated as a two phase circuit
• If channels 7, 9 and 11 have the same circuit number, e.g. 7, these will
be treated as a three phase circuit
• If the top bit of a three phase circuit is set, e.g. hexadecimal 8007
(32775 in decimal), then it is treated as being connected to a delta
load.
If this does not help, recommend contacting technical support for more assistance.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Anonymous user
I am assuming you are referring to https://www.se.com/ww/en/download/document/ZL0192-0A/ as protocol guide.
Looking at page 1 I see the following information:
"For simplicity, this document only deals with Modbus addresses using 0-based numbering. Modbus terminology puts register 1 is at address 0."
Per Circuit Registers
C = (channel number * 10) – where the channel number ranges from 1 to 192.
Register Value
C + 0 VRMS in 0.1V steps (other steps maybe configured in regs 4498-4501)
C + 1 Circuit number (for creating single, two, three or four phase circuits)
C + 2 IRMS in 10mA steps (other steps maybe configured in regs 4498-4501)
C + 3 CT Type
C + 4 Pfactor * 1000 (signed)
C + 5 Watts in 1W steps (other steps maybe configured in regs 4498-4501)
C + 6 CT Factor * 1000
C + 7 iTHD
C + 8 Phase (1, 2 or 3) - 0 is disconnected
C + 9 Expected phase (1, 2 or 3) – as programmed during setup
Examples:
• VRMS for circuit 1 would be address 10 (1 * 10) + 0
• Power factor for circuit 9 would be address 94 (9 * 10) + 4
C + 1 Circuit number
This number is used to indicate whether channels should be grouped together
as two phase or three phase circuits – or left as a single phase circuit.
Examples:
• Channels that have a unique circuit number will be treated as single
phase circuits.
• If channels 3 and 5 have the same circuit number, e.g. 3, these will be
treated as a two phase circuit
• If channels 7, 9 and 11 have the same circuit number, e.g. 7, these will
be treated as a three phase circuit
• If the top bit of a three phase circuit is set, e.g. hexadecimal 8007
(32775 in decimal), then it is treated as being connected to a delta
load.
If this does not help, recommend contacting technical support for more assistance.
Regards,
Charles