Problems with PM8000 using as a Modbus Master Gateway for Serial devices in PME

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Problems with PM8000 using as a Modbus Master Gateway for Serial devices in PME
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2018-03-02 02:59 AM

0 Likes
1
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-02 02:59 AM

Problems with PM8000 using as a Modbus Master Gateway for Serial devices in PME

Customer wants to use 3x PM8000 device as a master gateway for different slave meters.

The problem is we cant get a connection to the modbus slaves.

Also the devices are not seen in the ION-Setup and also the PM8000 itself could not be configured in ion Setup.

I set a site with the IP of the PM8000 and set a device with the Slave ID100 which should be the device itself.

As you can see - unable to upload device feature information

After flashing the newest firmware we could not see the ip configuration in the webapplication anymore but the device is reachable with the correct IP.

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2018-03-02 09:10 AM

2 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-02 09:10 AM

In most instances where you are communicating to a PM8000 via direct Ethernet (plugged directly via RJ-45), you will want to use IP port 7700, not 502 to communicate to the device (this uses ION protocol instead of Modbus TCP).  Firmware version 1.4.0 for the PM8000 while it does allow ION to operate over Modbus, this should only be used when the PM8K is being a device replacement in a serial RS-485 installation along with other Modbus devices (and adding a 2nd ION only RS-485 line isn't an option).

In this instance, you would want to add two sites in ION Setup, one for the PM8K itself (as a direct Ethernet device), and a Modbus gateway for any slaves devices attached to the PM8K Com1 RS-485 port.

So the above "ION Device 1" would be the PM8K directly, while the "ION Gateway Device 2" would be a slave device downstream.

Also to enable the PM8K to allow for Modbus Gateway to operate properly, you have to use ION Setup (or ION Designer) to configure this feature as it can't be properly turned on via the front panel or web interfaces right now.

If you have a more recent version of ION Setup, when you enable "Modbus Master" on the Com1 Port for the PM8K, ION Setup will now prompt if you want to turn on the gateway as well.

You can also control the Modbus Gateway via the default Setup Assistant under Communications -> Basic Ethernet -> TCP/IP.

It will give you the option to pick any port but will only indicate its operational if the protocol is Modbus Master.

See Answer In Context

Reply
Reply 1
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2018-03-02 09:10 AM

2 Likes
0
1483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-03-02 09:10 AM

In most instances where you are communicating to a PM8000 via direct Ethernet (plugged directly via RJ-45), you will want to use IP port 7700, not 502 to communicate to the device (this uses ION protocol instead of Modbus TCP).  Firmware version 1.4.0 for the PM8000 while it does allow ION to operate over Modbus, this should only be used when the PM8K is being a device replacement in a serial RS-485 installation along with other Modbus devices (and adding a 2nd ION only RS-485 line isn't an option).

In this instance, you would want to add two sites in ION Setup, one for the PM8K itself (as a direct Ethernet device), and a Modbus gateway for any slaves devices attached to the PM8K Com1 RS-485 port.

So the above "ION Device 1" would be the PM8K directly, while the "ION Gateway Device 2" would be a slave device downstream.

Also to enable the PM8K to allow for Modbus Gateway to operate properly, you have to use ION Setup (or ION Designer) to configure this feature as it can't be properly turned on via the front panel or web interfaces right now.

If you have a more recent version of ION Setup, when you enable "Modbus Master" on the Com1 Port for the PM8K, ION Setup will now prompt if you want to turn on the gateway as well.

You can also control the Modbus Gateway via the default Setup Assistant under Communications -> Basic Ethernet -> TCP/IP.

It will give you the option to pick any port but will only indicate its operational if the protocol is Modbus Master.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of