Problem with ION7550 and automatic reset of kWh?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Problem with ION7550 and automatic reset of kWh?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-05-19 02:24 AM . Last Modified: ‎2022-10-18 10:24 PM

0 Likes
3
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-19 02:24 AM

Problem with ION7550 and automatic reset of kWh?

Hello,

I have a problem with the ION7550 at system with very high consumption.

Does it reset by itself when reaching a very high value?

as you can see here from ION setup:

20:15 kWh del = 9962870

20:30 kWh del = 21597406

20:45 kWh del = 80347969

21:00 kWh del = 139086.66 ?

on Trend it looks like this:

there are some modifications done described  in

https://community.se.com/message/71714?commentID=71714#comment-71714

for MWh and GWh because of same Display problem.

And there are Modbus Slave Modules e.g. Register 230 for other Master System

Is it a Problem with the meter or a Problem with configuration?

Attached the energy demand of internal storage & Meter configuration file

On ION Reference I found this:

What is best Format fur such big values? At the moment Unsigned 32B is set, because this is the biggest possible ?

What is In Zero, In Full, OutZero and Out Full needed for?

What is the Rollover needed for?

thank you

Attachments
EnergyDemand Log for MI-1004A404-02.csv.zip
backup_7550_FAC_V3.4.0.0.0.dcf.zip
Tags (1)
  • Tags:
  • ion75507650
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
sesa64419
sesa64419 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-05-19 07:29 AM

0 Likes
0
767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-19 07:29 AM

Hi Sven

The reset in the kWh del is caused by rollover. Rollover is a setup register in the Integrator module, defined in the ION Reference as follows:

RollValue

When the Result output register reaches the value specified by the RollValue setup register, the Result output register will rollover (be reset to 0). Setting this register to zero disables the Rollover feature (no rollovers will occur).

There is also an output register called Rollover Count, which increments every time the rollover occurs.

The default rollover values are defined in the ION Device Template Reference, which you can download here:

http://www.schneider-electric.com/en/download/document/ION_Device_Templates_Reference_70090-0017/

More details on the Integrator and other ION modules are in the ION Reference, which you can download here:

http://www.schneider-electric.com/en/download/document/7EN02-0290/

Looking at your values and the default, it appears the rollover occurs more as a power of 10 then an actual value, as your rollover occurred when your value exceeded 10^8.

To confirm that this is caused by integrator rollover, you could look at the Rollover Count output register on the integrator before and after.

Hope this helps.

Cheers,

Alana

Reply
Yu_Diao
Commander Yu_Diao Commander
Commander

Posted: ‎2017-05-19 11:20 PM

0 Likes
1
767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-19 11:20 PM

As indicated above, with all the default value, the energy value will rest back to Zero when it reaches 10^8 kWh. I don't know the application here, but 10^8 is a large number and I don't understand how the rollover could happen so quick. I look at the Energy demand log, the difference of "kWh del-rec" between row 1776 and 1776 is 6576091, which means during that 15 minutes period alone, the load consumes 6576091 kWh. Is it a whole city or something?

Unfortuntly, I don't have a 7550 to load your dcf, but if there is any customization was done in the framework, I would double check that again.

Reply
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-06-12 01:40 AM

0 Likes
0
767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-12 01:40 AM

hello,

I have a remote Session today and will set the rollback to 0. I hope this solves the Problem.

The meter is installed in a power plant. This is why they have that high consumption. Would be perfect to configure the Meter by standard as MW GW consumption.But the only way is to connect the kw to a arithmetic tool and divide to e.g 1000 but the main value stays at kw so this is no good solution to be honest.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of