Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PowerTag A9MEM1570

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PowerTag A9MEM1570
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Patrick_Grehan
Patrick_Grehan
Explorer

Posted: ‎2024-10-18 04:22 AM

0 Likes
5
1798
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-18 04:22 AM

PowerTag A9MEM1570

Hi all,

 

Is it possible to use A9MEM1570 (3P + N) as a substitute for A9MEM15703 (3P) with neutral not connected? - Any feedback is appreciated.

 

Thanks.

Labels
  • Labels:
  • PowerTag Energy
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Jesus_Diaz
Jesus_Diaz Leader
Leader

Posted: ‎2024-10-22 12:36 PM

0 Likes
0
1738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-22 12:36 PM

Hi @Patrick_Grehan,

 

Yes, this will fall under the first case: when the neutral is not connected (on load and PowerTag), the data by phase will be incorrect if the phases are not well balanced, but the total power/energies will be accurate.

 

Regards,

JD

See Answer In Context

Reply
Replies 5
Jesus_Diaz
Jesus_Diaz Leader
Leader

Posted: ‎2024-10-21 11:55 AM

1 Like
1
1785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-21 11:55 AM

Hi @Patrick_Grehan ,

 

Without information about the location and installation of the PowerTag (PTag) and assuming it is a 3P +N system, we can make the following observations:

 

  • When the neutral is not connected (on load and PowerTag), the data by phase will be incorrect if the phases are not well balanced, but the total power/energies will be accurate.
  • When the neutral is connected on loads but PowerTag is not connected to neutral, then if the phases are not well balanced, the total power/energies will be incorrect (because even though we are monitoring the current, the voltage vector sum cannot be accurate as the neutral voltage is missing).

 

Best Regards,

JD

 

Reply
Patrick_Grehan
Patrick_Grehan
Explorer

Posted: ‎2024-10-22 01:18 AM

0 Likes
0
1758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-22 01:18 AM

Hi @Jesus_Diaz 

Thanks for your response - to clarify, my question was around using the PTag on a 3P load (no neutral). Installing the 3P+N PowerTag (A9MEM1570) without the neutral connected, as per your comment above, may see some inaccuracy in phase data (if unbalanced) but overall power / energy data will be accurate. Have I summarised your response accurately?

Thanks,

PG 

Reply
Jesus_Diaz
Jesus_Diaz Leader
Leader

Posted: ‎2024-10-22 12:36 PM

0 Likes
0
1738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-22 12:36 PM

Hi @Patrick_Grehan,

 

Yes, this will fall under the first case: when the neutral is not connected (on load and PowerTag), the data by phase will be incorrect if the phases are not well balanced, but the total power/energies will be accurate.

 

Regards,

JD

Reply
Romain_Polette
Romain_Polette Champion
Champion

Posted: ‎2024-10-22 11:11 PM

0 Likes
1
1718
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-22 11:11 PM

Hello @Patrick_Grehan , 

What are you going to do with the Neutral connector of your PowerTag F63 ?

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Patrick_Grehan
Patrick_Grehan
Explorer

Posted: ‎2024-10-23 02:45 AM

0 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-23 02:45 AM

Hi Romain,

The neutral would not be connected and insulated. My question is basically if it's appropriate to do this.

Thanks,

PG

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore