Hello everyone,
Are current inputs on ION device galvanicly isolated?
Thanks in advance.
Best Regards
- Labels:
-
ION9000
-
Power Quality
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
depends...
Yes. The standard (20Arms max) current input option of the ION9000 family are galvanically isolated with current transformers .
No, The LVCS (Low Voltage Current Sensor) current input option of the ION9000 family are galvanically connected (200 k-Ohm)
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @DanL ,
Do you know if the current inputs to ION9000 meter are galvanically isolated?
Regards,
Charles