New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Power Quality meters
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2014-10-3001:01 AM
Power Quality meters
Do we have a future plain to implement sampled value(with 61850-9.2 process bus) measuring inputs to some of revenue ION meters like ION 8800, ION7650, ION8650?
Link copied. Please paste this link to share this article on your social media post.
2014-10-3010:46 AM
On the technical side, we have looked at the process bus before. One of the challenges is the fact that standard sampling rates supported are significantly lower than the sampling rates used on these meters. Using the sampling rates outlined in the standard would likely result in degraded accuracy and limitations on PQ functions for these meters.
On the marketing side, I would defer to someone in offer creation for a formal answer. To my knowledge, though, there is no immediate plan to implement it on these meters.
If you have knowledge of a customer application that would benefit from this feature, I would be very interested to hear more!
Link copied. Please paste this link to share this article on your social media post.
2015-01-1501:00 AM
This issue reminds me of what the utility told me that our competitor L&G had informed them that they have just developed the revenue meter that work on process bus accurately. Then I commented that our sampling rate is higher than the merging unit do they agree with me and said "oh yes you are right the high accuracy on low resolution signal".