Continue
  • My Subscriptions
  • Events
Power Meter
Metering & Power Quality
  • EcoStruxure Power & Grid
  • Power Meter
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
PeterB69
PeterB69
Explorer
Posted: ‎2024-02-07 09:19 AM
1524
Power Meter
We have 1 DB on a site of 20 plus DB's that the meter is not converting the amps/volts into KWH correctly. It is a split metered DB with 2No A9MEE3255 installed. We are only getting recorded values of a few kilowatts when it should be a lot more. We have changed the meter for new one and checked all the wiring but can't see any issue. I am out of ideas if anyone can help
  • PowerTag Energy
Jesus_Diaz
Jesus_Diaz Leader
Leader
Posted: ‎2024-07-19 03:24 PM . Last Modified: ‎2024-07-19 03:24 PM
What type of load are you using?
I suggest contacting your local support as we may need more information to provide you with a better answer.
Charles_Murison
Champion
Posted: ‎2024-07-19 08:43 AM
Hello @Jesus_Diaz ,
Do you have any idea for should customer reach out to local technical support?
Charles
Jesus_Diaz
Jesus_Diaz Leader
Leader
PeterB69
PeterB69
Explorer
Posted: ‎2024-07-23 12:34 AM
Problem solved. It turned out to be the top (Lighting) section of the split load DB voltage connections had been connected wrong (V1-V3-V2) in the factory and this was causing the meter to read incorrectly. Swoped cable around to V1-V2-V3 and meter began to record correctly.