Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Power Meter Onboard Alarm Issue

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Power Meter Onboard Alarm Issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
William_Tournas
Lieutenant JG William_Tournas Lieutenant JG
Lieutenant JG

Posted: ‎2018-09-13 10:32 PM . Last Modified: ‎2023-03-27 07:21 AM

2 Likes
1
1103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-09-13 10:32 PM

Power Meter Onboard Alarm Issue

Hi All, my customer is having issues with onboard alarms for a PM8000 device, but their query is about all power meter onboard alarms.

 

The issue is that this was an alarm generated because there was no voltage being read by the meter, which is normal operating mode for the meter on the generator supply. Unfortunately, disabling this alarm (as it is not needed) did not cause the alarm to be cleared. It stayed as an active alarm on both the meter and the SCADA that was interfacing with it.

 

The way we know the clear these alarms is to put the power meter into a state which identifies the alarms in a healthy state. Eg the example above is a voltage disturbance alarm. The power meter is always at 0 volts as it is a generator feed power meter. Therefore the only way to clear the alarm was to turn the generator system on to allow the power meter to meet the voltage requirements which is 230 volts for voltage disturbance. then to disable the alarm for it to not come back. 

 

This will be a big issue if my customer has to go and retrofit any more generator meters as they will get alarms when the meter is installed, because it is enabled by default.

 

Is there plans to solve the above issues by introducing a reset feature of some sort?

Labels
  • Labels:
  • PM8000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Anonymous user
Not applicable

Posted: ‎2018-09-17 01:05 PM

0 Likes
0
1092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-09-17 01:05 PM

Not sure if this will be helpful or not. On QED2 switchboard we have had customers request voltage taps on the load side. With voltage taps on the load side the meter is always powered. The CTs are still reading zero so power readings should stay very close to zero. 

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of