Per phase power demand using PM8000 or ION9000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Per phase power demand using PM8000 or ION9000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
523
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
138
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
TC
Crewman TC Crewman
Crewman

Posted: ‎2025-11-24 06:09 PM . Last Modified: ‎2025-11-24 06:12 PM

0 Likes
3
58
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-24 06:09 PM

Per phase power demand using PM8000 or ION9000

Hi,

 

Working on a request from customer to obtain information pertaining to below via MODBUS.

It seems, address 30222 reflect 3-phase data instead of phase A.

Whereas for address 30236 and 30250, no valid data available.

This is observed both in PM8240 and ION9000.

Firmware upgraded to latest.

Also tried various voltage mode. 

 

Active Power Del A Last Demand [ Modbus 30222 ]

Active Power Del B Last Demand [ Modbus 30236 ]

Active Power Del C Last Demand [ Modbus 30250 ]

 

Would expect above very much collated to Active Power A,B,C.

But instead, the observation is 30222 reflect total of 3054 + 3056 + 3058

Active Power A [ Modbus 3054 ]

Active Power B [ Modbus 3056 ]

Active Power C [ Modbus 3058 ]

 

Any advice? 

Attachments
Labels
  • Labels:
  • ION9000
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-11-24 09:16 PM

0 Likes
0
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-24 09:16 PM

Hello @TC ,

30222 , 30236 and 30250 these measurements are not per phase values but Rates A, Rate B, Rate C and Rate D (30264).

The default Modbus register list does not have the measurement you are looking for. With the power of ION, it is possible to make a custom framework that is able to get the information you are looking for and link to new Modbus registers.

You would need to make 3 sliding windows demand modules (SWD), linking the per phase kw readings from the power meter module. The output of the SWD module can be linked to new Modbus Slave Modules.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Reply
TC
Crewman TC Crewman
Crewman

Posted: ‎2025-11-24 09:22 PM

0 Likes
0
44
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-24 09:22 PM

Thank you @Charles_Murison .

Very clear. 

Reply
TC
Crewman TC Crewman
Crewman

Posted: ‎2025-11-25 07:28 PM

0 Likes
0
8
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-25 07:28 PM

Hi all, working on the full expectation of customer and hoping to get some advice:

The requirement is "At the end of demand interval, to report the min, max, average of each phase. kW and kVA".

 

What is the most optimized way to achieve this?

 

Currently exploring with min, max, and ave module which is not exactly matching the expectation. 

Struggling with the need to add "processing" so that the values are reported only once at end of demand interval, before resetting. 

 

Hope to get some guidance. Thank you!

(I have attached PPT, and video for better grasp of my situation) 

Attachments
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore