Acti 9 iEM3255 rogowski coils
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
No, you cannot change the 1167 µV/kA/Hz value because it is a fixed physical property of the Rogowski coil, not a configurable setting in the meter.
Please note that, iEM3255 does NOT support Rogowski coils and it only works with standard external CTs (1 A or 5 A). Rogowski coils require meters with an integrator circuit to interpret their voltage signal, which iEM3255 does not have.
Models that support Rogowski coils include iEM3555, iEM3565, and some iEM3400/iEM3500 series variants.
No, you cannot change the 1167 µV/kA/Hz value because it is a fixed physical property of the Rogowski coil, not a configurable setting in the meter.
Please note that, iEM3255 does NOT support Rogowski coils and it only works with standard external CTs (1 A or 5 A). Rogowski coils require meters with an integrator circuit to interpret their voltage signal, which iEM3255 does not have.
Models that support Rogowski coils include iEM3555, iEM3565, and some iEM3400/iEM3500 series variants.