Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

PME Web Application : Alarms

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PME Web Application : Alarms
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
SD23
Crewman SD23
Crewman

Posted: ‎2024-03-06 12:46 AM

0 Likes
2
958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-03-06 12:46 AM

PME Web Application : Alarms

Hello, I am working with PME 2023, I have created a device within DTE and added additional Digital Input registers. now that I want to create Alarm rules (within Web application) for those inputs, I am not able to set the rules for the new registers created. Only the predefined registers are shown. Can someone help me with this ?

Tags (7)
  • Tags:
  • AlarmRules
  • alarms
  • dte
  • english
  • IONhandle
  • PME2023
  • web application
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Rafaela_Cordeiro
Lt. Commander Rafaela_Cordeiro Lt. Commander
Lt. Commander

Posted: ‎2024-03-20 09:54 AM

1 Like
0
925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-03-20 09:54 AM

Hi,

Sometimes it takes time for the web application to recognize the links of a custom measurement for a custom driver. 

You may want to enable the PC based logs for these new inputs (https://digital-energy-help.se.com/pme/content/8_reference/configuring/dte/dte_configloggingcalcui.h...) and let them log for at least one interval - you can disable the logs later as you wish. 

This should allow you to see the new measurement in the Web App for selection. 

 

If you still face an issue, I recommend reaching out to your local tech support for further assistance.

https://www.se.com/ww/en/work/support/country-selector/contact-us.jsp 

See Answer In Context

Reply
Replies 2
Rafaela_Cordeiro
Lt. Commander Rafaela_Cordeiro Lt. Commander
Lt. Commander

Posted: ‎2024-03-20 09:54 AM

1 Like
0
926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-03-20 09:54 AM

Hi,

Sometimes it takes time for the web application to recognize the links of a custom measurement for a custom driver. 

You may want to enable the PC based logs for these new inputs (https://digital-energy-help.se.com/pme/content/8_reference/configuring/dte/dte_configloggingcalcui.h...) and let them log for at least one interval - you can disable the logs later as you wish. 

This should allow you to see the new measurement in the Web App for selection. 

 

If you still face an issue, I recommend reaching out to your local tech support for further assistance.

https://www.se.com/ww/en/work/support/country-selector/contact-us.jsp 

Reply
SD23
Crewman SD23
Crewman

Posted: ‎2024-03-26 09:52 AM

1 Like
0
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-03-26 09:52 AM

Thanks Rafaela for your reply, I was able to solve my issue by enable logs and using the designer.

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of