Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM850 waveform association with an alarm

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM850 waveform association with an alarm
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Sven_Ortmann
Sven_Ortmann Leader
Leader

Posted: ‎2014-10-16 06:31 AM

0 Likes
2
1212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-10-16 06:31 AM

PM850 waveform association with an alarm

Hi,

how is it possible to associate a waveform with an alarm at an PM 850?

i read about it but i did not fint settings in ION Setup

4945

4944

Here i have some events with waveform but no alarms

4946

4947

on the device i can see the waveforms, but how can i connect the waveforms to see direktly with one klick on alarms?

4948

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2014-10-16 10:13 AM

0 Likes
0
1162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-10-16 10:13 AM

Waveforms and alarms are actually independent of each other.  What this means is that just because there is an alarm there may or may not be an associated waveform.  Also vice versa.  Note that an alarm *may* trigger a waveform capture but this is dependent on the device configuration.  Likewise a waveform can be triggered without an associated event (like a manual trigger).

What the software does to associate the two types of log data is to match the timestamps of the event and the waveform (or data log) and display them together.  This is done through a custom log query request.  For examples have a look at the log queries on the default Vista diagrams.  The devices with PQ typically do this sort of query so they would be a good first place to look (ie the PQ specific diagrams).  Typical diagram log queries are much simpler - much like a tabular report - just query a particular measurement for that source and display all timestamped values.  The PQ log queries do additional filtering and joining of multiple measurements to display a more complete system view of the PQ incident.

See Answer In Context

Reply
Replies 2
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2014-10-16 09:02 AM

0 Likes
0
1162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-10-16 09:02 AM

Hi Sven,

For the older PowerLogic devices, associating waveforms to an alarm is just a means to say that when an alarm occurs, that it will trigger a waveform capture.  This can be done using ION Setup (or PMCU) via the Onboard Alarms/Events setup dialog.  There is a checkbox that appears near the bottom of the alarm options which indicate if you wish to trigger a waveform capture if the alarm goes active.

4952
When our PME software downloads the meter events and waveforms, it will then see that the two pieces of data are somewhat connected and show the icon as you've stated.  Manually triggered waveforms however will not appear in such a manner nor can you assign them to events after the fact (not that I know of but maybe some one from the PME team can clarify if it is possible).

Reply
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2014-10-16 10:13 AM

0 Likes
0
1162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-10-16 10:13 AM

Waveforms and alarms are actually independent of each other.  What this means is that just because there is an alarm there may or may not be an associated waveform.  Also vice versa.  Note that an alarm *may* trigger a waveform capture but this is dependent on the device configuration.  Likewise a waveform can be triggered without an associated event (like a manual trigger).

What the software does to associate the two types of log data is to match the timestamps of the event and the waveform (or data log) and display them together.  This is done through a custom log query request.  For examples have a look at the log queries on the default Vista diagrams.  The devices with PQ typically do this sort of query so they would be a good first place to look (ie the PQ specific diagrams).  Typical diagram log queries are much simpler - much like a tabular report - just query a particular measurement for that source and display all timestamped values.  The PQ log queries do additional filtering and joining of multiple measurements to display a more complete system view of the PQ incident.

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore