Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to get PM870 waveform w/o PME software?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • How to get PM870 waveform w/o PME software?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
202
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2013-10-21 07:18 PM

1 Like
7
2688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-21 07:18 PM

How to get PM870 waveform w/o PME software?

Is the waveform accessible through PM8ECC embedded web server?

Thanks

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa111809_brid
sesa111809_brid Leader
Leader

Posted: ‎2013-10-22 09:24 AM

1 Like
4
2431
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-22 09:24 AM

Abon

Waveform captures can be accessed using ION Setup software.

Status:

Select the appropriate option to enable or disable this feature.

File Mode:

Select which method is used for storing waveforms:

  “FIFO” (first-in-first-out) mode discards the oldest waveform capture when the waveform storage is full.

  “Fill and Hold” mode keeps the oldest waveform capture and does not record new ones when the waveform storage becomes full.

Channels (PM870 only)

This allows you to select which inputs you want to set up for waveform capture.

Select “Channels” then click Edit.

Depending on your wiring configuration, certain inputs become N/A (not applicable). If this is the case, ION Setup displays this prompt:

1. Select the voltage and/or current input channels you want to capture. Click Next.

2. Set the capture options:

       Samples/Cycle

       Duration (cycles)

       Pre-Event Cycles


       Max Capture indicates the maximum number of recordings for waveform capture, and is shown for informational purpose only.

See Answer In Context

Reply
Replies 7
sesa111809_brid
sesa111809_brid Leader
Leader

Posted: ‎2013-10-22 09:24 AM

1 Like
4
2432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-22 09:24 AM

Abon

Waveform captures can be accessed using ION Setup software.

Status:

Select the appropriate option to enable or disable this feature.

File Mode:

Select which method is used for storing waveforms:

  “FIFO” (first-in-first-out) mode discards the oldest waveform capture when the waveform storage is full.

  “Fill and Hold” mode keeps the oldest waveform capture and does not record new ones when the waveform storage becomes full.

Channels (PM870 only)

This allows you to select which inputs you want to set up for waveform capture.

Select “Channels” then click Edit.

Depending on your wiring configuration, certain inputs become N/A (not applicable). If this is the case, ION Setup displays this prompt:

1. Select the voltage and/or current input channels you want to capture. Click Next.

2. Set the capture options:

       Samples/Cycle

       Duration (cycles)

       Pre-Event Cycles


       Max Capture indicates the maximum number of recordings for waveform capture, and is shown for informational purpose only.

Reply
Anonymous user
Not applicable

Posted: ‎2013-10-22 04:55 PM

1 Like
2
2431
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-22 04:55 PM

Barry,

Thanks for your reply.

I'm thinking about writing a script to implement what you suggested with IONSetup and get captured waveform file( JPEG?) in a specific directory that BMS can access.

Sent from mobile

"Barry Cantrell" <powersolutionscommunity-admin@powersolutionscommunity.hosted.jivesoftware.com> 於 2013/10/23 0:10 寫道:

Solutions Expert Community

How to get PM870 waveform w/o PME software?

reply from Barry Cantrell in Power Monitoring Hardware - View the full discussion

Abon

Waveform captures can be accessed using ION Setup software.

Status:

Select the appropriate option to enable or disable this feature.

File Mode:

Select which method is used for storing waveforms:

“FIFO” (first-in-first-out) mode discards the oldest waveform capture when the waveform storage is full.

“Fill and Hold” mode keeps the oldest waveform capture and does not record new ones when the waveform storage becomes full.

Channels (PM870 only)

This allows you to select which inputs you want to set up for waveform capture.

Select “Channels” then click Edit.

Depending on your wiring configuration, certain inputs become N/A (not applicable). If this is the case, ION Setup displays this prompt:

1. Select the voltage and/or current input channels you want to capture. Click Next.

2. Set the capture options:

Samples/Cycle

Duration (cycles)

Pre-Event Cycles

Max Capture indicates the maximum number of recordings for waveform capture, and is shown for informational purpose only.

Reply to this message by replying to this email, or go to the message on Solutions Expert Community

Start a new discussion in Power Monitoring Hardware by email or at Solutions Expert Community

Following How to get PM870 waveform w/o PME software? in these streams: Inbox

>

Reply
sesa72458
sesa72458 Leader
Leader

Posted: ‎2013-10-30 09:11 PM

0 Likes
0
2431
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-30 09:11 PM

Hi Abon,

Please keep us updated with how you go with this, I have a customer who is interested in a similar solution. They want to use our meters but refuse to use SPME.

I'm also keen to understand if it will be possible to access the sag/swell/transient waveforms via the same method?

Regards,

Steven Yan

Reply
sesa50168
sesa50168 Leader
Leader

Posted: ‎2013-10-31 07:33 AM

1 Like
0
2432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-31 07:33 AM

Hi Abon -

I'll be interested in what you learn when you investigate the waveform display function of ION Setup.  I don't know how this is done, but I guess that it reads the Modbus registers in the meter and then maps/displays the data.  I do know that we have not publicly released the meter's Modbus mapping of the waveforms.

Regards,

John Straughn

Reply
Sven_Ortmann
Sven_Ortmann Leader
Leader

Posted: ‎2014-10-13 04:04 AM

0 Likes
1
2432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-10-13 04:04 AM

hi all,

are there any news? I am also interessted in this captured waveform file.

Reply
Sven_Ortmann
Sven_Ortmann Leader
Leader

Posted: ‎2014-10-16 06:18 AM

0 Likes
0
2432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-10-16 06:18 AM

Hi,

how can i enable the Waveform feature with ION Setup?

4942

4943

Reply
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2014-10-16 10:01 AM

1 Like
0
2432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-10-16 10:01 AM

Please this thread for information regarding reading the PM800 waveform.

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore