PM8240 meter modbus register 30108 Issues after firmware update

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8240 meter modbus register 30108 Issues after firmware update
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
JarrydWebber
Ensign JarrydWebber
Ensign

Posted: ‎2023-08-02 04:19 AM

0 Likes
2
913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-02 04:19 AM

PM8240 meter modbus register 30108 Issues after firmware update

Good day all

We have recently performed some updates on our PM8240 meters, updating the firmware, from V2.1 and V3 up to the latest V4.0.0
We have noted that the performance of the values reported on modbus register 30108 have changed.
Register 30108 is mapped to "Apparent Power Total Last Demand".

In the below screen capture of a log of this register, the behavior changed on the 30th June.

JarrydWebber_0-1690975073566.png

 

Before the update the log was reporting consistently high values (~1200 kVA) while after the update it reports ~10kVA and occasionally jumps to the previous high values.

The setup of the meter is exactly the same as it was, and we have compared it against meters that we have not updated yet, and the ion settings are the same.

Does anyone have any indication as to what might be happening here?

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-08-02 09:34 AM

0 Likes
1
906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-02 09:34 AM

Hello @JarrydWebber ,

 

Hard to say what is happening from a picture alone. How often are you polling the modbus address? Would suggest tracing the information back through the meter's framework. Mapping from Modbus register to ION register is done through a number of mapping modules. For Modbus address 30108, this is Data mapping demand module. The ION register, "kVA sd del+rec" comes from a sliding window demand module. Would need to look at the output of this module to understand what is happening. It could be that this module update rate changed from end of interval to every second, it could be this module is linked to a reset. Hard to say for sure.

 

Can use ION Setup to investigate. Connect to the meter and change to advanced view. (Hold ctrl + click on meter in left panel. Setup Assistant needs to be closed.) Navigate to SWinDemand Modules -> kVA sd del+rec. Hold down shift and click on the tab Output registers, you should see the real time values each time you click. Right click on output registers and change the update rate, I would suggest 5 or every second. Watch the value of kVA sd del+rec and compare behavior between meters.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-08-02 09:34 AM

0 Likes
1
907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-02 09:34 AM

Hello @JarrydWebber ,

 

Hard to say what is happening from a picture alone. How often are you polling the modbus address? Would suggest tracing the information back through the meter's framework. Mapping from Modbus register to ION register is done through a number of mapping modules. For Modbus address 30108, this is Data mapping demand module. The ION register, "kVA sd del+rec" comes from a sliding window demand module. Would need to look at the output of this module to understand what is happening. It could be that this module update rate changed from end of interval to every second, it could be this module is linked to a reset. Hard to say for sure.

 

Can use ION Setup to investigate. Connect to the meter and change to advanced view. (Hold ctrl + click on meter in left panel. Setup Assistant needs to be closed.) Navigate to SWinDemand Modules -> kVA sd del+rec. Hold down shift and click on the tab Output registers, you should see the real time values each time you click. Right click on output registers and change the update rate, I would suggest 5 or every second. Watch the value of kVA sd del+rec and compare behavior between meters.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities
Reply
JarrydWebber
Ensign JarrydWebber
Ensign

Posted: ‎2023-08-03 01:02 AM

0 Likes
0
889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-03 01:02 AM

Hi Charles

Thank you so much for the advice.
It seems as though the firmware update changed the SD3 Update Rate to Each Second, while it was set to "End of Sub-Interval" previously.

It seems like this has resolved the issue. Thank you

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of