Hello @Stuart_Cheng ,
Sadly not possible to view waveforms from the front panel of ION meters. The ION9000 and PM8000 do support COMTRADE files for waveform capture, that is another option other than what you have already listed.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Stuart_Cheng ,
Sadly not possible to view waveforms from the front panel of ION meters. The ION9000 and PM8000 do support COMTRADE files for waveform capture, that is another option other than what you have already listed.
Regards,
Charles