Hello,
Is there a recommended manufacturer for ferrule terminals to be connected to PQM voltage circuits, etc?
I explain to the customer that I just need to be careful about the thickness and length of the connections, but the customer wants Schneider's opinion just to be sure.
Reference: GDE41422-04
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @Miyai
We recommend the size of the ferrule terminals for current terminals, not the manufacturing part number.
As you explained, the suitable cylinder type lugs to be selected from any manufacturer based on the thickness and length of the connections for other terminals.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello @Miyai
We recommend the size of the ferrule terminals for current terminals, not the manufacturing part number.
As you explained, the suitable cylinder type lugs to be selected from any manufacturer based on the thickness and length of the connections for other terminals.
Regards,
Ramasamy N