Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Hi Team
Please may I ask you to verify if it is possible to simultaneously use the 2 x Ethernet Ports with IEC61850 and also the RS485 Port with Modbus RTU (ie can customer use all three ports simultaneously from different Masters)? for PM8240.
thanks
Link copied. Please paste this link to share this article on your social media post.
Hello @Gladwin ,
Yes it is possible for the meter to use multiple ports at the same time. One item to not is that both Ethernet ports are the same IP and cannot be isolated networks. If you connect 2 different networks the meter will bridge them. Note that meter supports multiple Port connections on 1 Ethernet connection.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Gladwin ,
Yes it is possible for the meter to use multiple ports at the same time. One item to not is that both Ethernet ports are the same IP and cannot be isolated networks. If you connect 2 different networks the meter will bridge them. Note that meter supports multiple Port connections on 1 Ethernet connection.
Regards,
Charles
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.