I5 Residual Ground Current Calculation for 1PH3W LL with N connection

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • I5 Residual Ground Current Calculation for 1PH3W LL with N connection
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
BrandonReed
Crewman BrandonReed
Crewman

Posted: ‎2024-07-27 03:12 PM

0 Likes
3
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-27 03:12 PM

I5 Residual Ground Current Calculation for 1PH3W LL with N connection

I have a PM8000 installed on a 120/240V single phase system. I have 3 CTs, one installed on each line, and one installed on the neutral (wired as shown in the attached picture).

 

I was expecting to see a residual ground current calculated as G= -(L1+L2+N) appear on the PM8000 internal webpage, but the value is always 0.000A. When I manually calculate the residual current using the magnitudes and angles from the phasor view, I get between 0.10A and 0.34A (depending on the instantaneous load). 

 

Tech support indicated this setup should work, as well as some unofficial confirmation from this post. 

 

Can someone point me in the right direction to get this working?

Thanks!

Attachments
Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2024-07-29 03:03 PM . Last Modified: ‎2024-07-29 03:04 PM

0 Likes
0
916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-29 03:03 PM

technically "no", but practically (in most cases) "yes"

 

in "Single" volts mode, there are two main categories of wiring CTs on the PM8000 family:

a) 2 CTs on each of two hot current carrying conductors (wired to I1 and I2. I3 not connected)

b) 1 CT on one hot current carrying conductor (wired to I1 only. I2 and I3 not connected)

For either case, if I4 is wired to an additional CT on a Neutral conductor (or I4 is wired as a summation of the other CTs as shown in a technote), then I5 is the (calculated) residual ground current, otherwise I5 is the (calculated) residual Neutral current

See Answer In Context

Reply
Replies 3
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-07-29 02:01 PM

0 Likes
1
923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-29 02:01 PM

Hello @DanL 

Do you know if the meter's calculation for I5 changes if meter is in Single Volts mode?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2024-07-29 03:03 PM . Last Modified: ‎2024-07-29 03:04 PM

0 Likes
0
917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-29 03:03 PM

technically "no", but practically (in most cases) "yes"

 

in "Single" volts mode, there are two main categories of wiring CTs on the PM8000 family:

a) 2 CTs on each of two hot current carrying conductors (wired to I1 and I2. I3 not connected)

b) 1 CT on one hot current carrying conductor (wired to I1 only. I2 and I3 not connected)

For either case, if I4 is wired to an additional CT on a Neutral conductor (or I4 is wired as a summation of the other CTs as shown in a technote), then I5 is the (calculated) residual ground current, otherwise I5 is the (calculated) residual Neutral current

Reply
BrandonReed
Crewman BrandonReed
Crewman

Posted: ‎2024-07-30 03:53 PM

0 Likes
0
836
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-30 03:53 PM

Hi @DanL, I have the meter wired per method (a) as described in your post, which also matches the wiring diagram I attached to this thread. However, I am not seeing any values populate for I5 on the meter's internal webpage (see other images attached to this thread). Can you point me in the right direction of what to check?

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of