Sur site on a des PM8000 en V3.0.0
Lorsque l'on veut se connecter avec ION Setup, il y a un message
"Found an ION meter still in upgrade mode.
Do you wish to continue upgrading?
Oui ou Non"
Quand on clic sur non, on ne vas pas plus loin.
Quand on click sur Oui, on demande une mise à jour en .ZIP ou un fichier en .UPG
le Zip ne fonctionne pas
et dans les versions supérieures il n'y a que des UPX, pas UPG
Si quelqu'un a une piste, nous sommes intéressés.
Link copied. Please paste this link to share this article on your social media post.
Hello @Olivier_GARAULT ,
Likely you are trying to use single device mode. If this is correct, try using the network mode. At the start before logging in be sure that Single ION device configuration mode is unchecked.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Olivier_GARAULT ,
Likely you are trying to use single device mode. If this is correct, try using the network mode. At the start before logging in be sure that Single ION device configuration mode is unchecked.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello Charles
Thanks a lot,
I think you had a call with my collegue too.
Regards,
Olivier