Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Meters for machines

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Meters for machines
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
geir_eas_no_bfo
geir_eas_no_bfo
Troubleshooter

Posted: ‎2025-09-05 03:55 AM

0 Likes
4
2594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-05 03:55 AM

Meters for machines

Hi,

 

I have a customer that is a manufactering factory in food business. 

 

I want a meter with rogowski coils that also include basic power Quality like THD and THDI.

Why can`t Powertag Rope measure this?

 

Schneider does not have a meter anymore in the "basic range" that can be installed "live" with rogoswski, or LVCT in thight spaces. 

 

Or am I wrong?

Do you have a suggestion ?

 

 

BR

GIA

Labels
  • Labels:
  • PowerTag Energy
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-09-05 11:22 AM . Last Modified: ‎2025-09-05 12:28 PM

0 Likes
0
2576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-05 11:22 AM

Hi @geir_eas_no_bfo 

 

The PowerTag Energy Rope is designed primarily for basic energy monitoring (voltage, current, power, power factor), but not for power quality analysis like THD.

 

- EM3570 Supports Rogowski CTs directly but not recommended for high harmonic environments.
- iEM3555 / iEM3565 (iEM3400/iEM3500 Series) are compatible with LVCT and Rogowski coils, but THD capabilities are limited and suitable for basic monitoring.
- PM5310R and PM5320R are designed to work with LVCTs, which measures Harmonics(up to 31st harmonics) and THD and TDD.

 

I recommend contacting your local sales team for better assistance based on your specific requirements.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 4
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-09-05 11:22 AM . Last Modified: ‎2025-09-05 12:28 PM

0 Likes
0
2576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-05 11:22 AM

Hi @geir_eas_no_bfo 

 

The PowerTag Energy Rope is designed primarily for basic energy monitoring (voltage, current, power, power factor), but not for power quality analysis like THD.

 

- EM3570 Supports Rogowski CTs directly but not recommended for high harmonic environments.
- iEM3555 / iEM3565 (iEM3400/iEM3500 Series) are compatible with LVCT and Rogowski coils, but THD capabilities are limited and suitable for basic monitoring.
- PM5310R and PM5320R are designed to work with LVCTs, which measures Harmonics(up to 31st harmonics) and THD and TDD.

 

I recommend contacting your local sales team for better assistance based on your specific requirements.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
geir_eas_no_bfo
geir_eas_no_bfo
Troubleshooter

Posted: ‎2025-09-08 06:45 AM

0 Likes
0
2555
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-08 06:45 AM

Hi, 

Got some new info today! It seems that PM5xxx will be relased shortly with Rogowski. This will be accordians with my requirments regarding Harmonics:)

BR

GIA

Reply
geir_eas_no_bfo
geir_eas_no_bfo
Troubleshooter

Posted: ‎2025-10-03 12:31 AM

0 Likes
0
2508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-03 12:31 AM

Hi, 

Seems that the rogowski vs PM5xxx was wrong. Someone from SE missunderstood.   

 

To solve this case regarding PM5xxx vs splitcore transformers: 

Could we use RJ45 Adapter on a PM5320R (QuickClick) and use a splitcore LVCT?

for instance LVCT00202S 

If so, where to find elctrical chema?

 

 

geir_eas_no_bfo_0-1759476266676.png

BR

GIA

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-10-28 09:08 AM

0 Likes
0
2340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-28 09:08 AM

Hi @geir_eas_no_bfo 

 

 

Even if you wire a non recommended LVCT via the RJ45 adapter, it’s not officially supported, and accuracy or safety could be compromised.

 

Best practice: Use one of the listed LVCT series (METSECTV250xx, 290xx, 350xx, 450xx).

 

PowerLogic™ PM53xxR series user guide

 

Mehran_Mehrnia_0-1761667598598.png

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore