Hello, I would like to open a case that happen when editing the analog values of a DNP map for an ION7550. When selecting a deadband of 5 or 1 instead of 10, for example, for each of the voltages seen in the attached image, an error appears indicating that I am requiring the use of too many modules and does not allow me to continue modifying the deadband. I would like to know if there is a correct configuration for this and to be able to avoid this error that appears or in any case if there is any recommendation or manual that we can follow to enable the DNP 3.0 protocol in ION meters. Greetings.
Link copied. Please paste this link to share this article on your social media post.
Hello @danielbarrantes ,
Need to take a step back and understand what ION Setup is trying to do. The DNP Slave Export Module has a maximum of 4 inputs. The setup registers, static object, event object, event class, scaling and others apply to all four inputs. Therefore if points next to each other have different scaling, 2 different DNP slave export modules would be needed. If you repeat this enough times you could end up with a configuration where almost all measurements use a different slave module. ION7550 meter support a maximum of 25 DNP slave export modules. If you are able to arrange measurement point maps where the same event class, scaling etc. are next to each others, you may be able to have the same number of measurements but with less DNP slave modules used.
Refer to ION reference for all of the setup registers used in the DNP slave export module. Note that not all ION meters support all registers.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @danielbarrantes ,
Need to take a step back and understand what ION Setup is trying to do. The DNP Slave Export Module has a maximum of 4 inputs. The setup registers, static object, event object, event class, scaling and others apply to all four inputs. Therefore if points next to each other have different scaling, 2 different DNP slave export modules would be needed. If you repeat this enough times you could end up with a configuration where almost all measurements use a different slave module. ION7550 meter support a maximum of 25 DNP slave export modules. If you are able to arrange measurement point maps where the same event class, scaling etc. are next to each others, you may be able to have the same number of measurements but with less DNP slave modules used.
Refer to ION reference for all of the setup registers used in the DNP slave export module. Note that not all ION meters support all registers.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello, I am having a similar problem.
I have added the necessary signals, but I left some indexes empty. For example, the last existing index is 58, and I started adding from 75. After processing the modules, it can be seen that ION Setup has rebuilt the original modules, and several of the new modules are now offline. What could be the problem? Also, what is the limit for modules or signals? Can the same signal be used in two different DNP3 points, for example, Vll ab at point 0 and also at point 75?
Link copied. Please paste this link to share this article on your social media post.
Hello @Sergio_Garcia ,
The limit of modules may be meter or firmware specific. Different meter types and firmware versions may have different limits to the number of modules supported. Also depending on the meter template, the CPU usage or total load may not be able to handle additional modules even if the maximum number of modules has not been reached yet.
You can have the same handle linked to multiple DNP export modules. The base point in the module does not have to be sequential for the module to go online.
In advanced mode, you may see a message in the bottom left indicating why the module cannot go online.
Regards,
Charles