Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000 residual current modbus register

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 residual current modbus register
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
kantiarion
kantiarion
Explorer

Posted: ‎2024-01-01 09:30 AM

0 Likes
3
1932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-01 09:30 AM

PM8000 residual current modbus register

Hello.

The current setup:

SE PM8240 SW 4.5.0 Standard, 4W-WYE, 4CT connected.

I want to read residual current calc value, and I suppose it is I5 (modbus register 3008) but the value is approximatively the same as I4. And if I do I4-I5 i obtain a value ~20mA so i supposes this is the residual current.

I read the modbus register map xlsx and I find "Residual current I0 sum" (modbus register 3094) but with wrong value(-4.591774807899561e-41). What is this register reading in fact?

It is a possibility to read residual current calculated directly from a modbus register?

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-01-05 01:17 PM

1 Like
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-05 01:17 PM

Hello @kantiarion ,

 

Remember that when you are looking at currents from the web page or display etc. you are looking at 1 second RMS values. The calculated residual current you can think of the sample by sample summation of -(I1+I2+I3+I4). Then I5 as seen on web pages display etc. is the RMS of these calculate samples. You cannot look at the RMS currents and do math on those number expecting to be able to predict the value of I5. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-01-02 03:00 PM

0 Likes
2
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-02 03:00 PM

Hello @kantiarion ,

 

The PM8000 does not have a Residual current I0 sum calculation. This specific register exists on the ION9000. I will forward this observation to the firmware team responsible for generating the modbus map file. For the PM8000, the Residual current calculation would indeed be I5. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
kantiarion
kantiarion
Explorer

Posted: ‎2024-01-04 06:20 AM

0 Likes
1
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-04 06:20 AM

Then something is not right with I5 calculation. The value of I5 is almost the same as measured value of I4 +-50mA I verify the connection again and nothing is wrong. The strange think is if I invert polarity of I4 the I5 is double I4. So how is calculated I5 current?

Attachments
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-01-05 01:17 PM

1 Like
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-05 01:17 PM

Hello @kantiarion ,

 

Remember that when you are looking at currents from the web page or display etc. you are looking at 1 second RMS values. The calculated residual current you can think of the sample by sample summation of -(I1+I2+I3+I4). Then I5 as seen on web pages display etc. is the RMS of these calculate samples. You cannot look at the RMS currents and do math on those number expecting to be able to predict the value of I5. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore