Following setting up a METSEHDPM6S480VD i am receiving A(rms) values which are double the measured current when using a handheld clamp meter , is there setting i need to alter
Link copied. Please paste this link to share this article on your social media post.
Hello @Bobhow1
Can you please verify the installed CT part number and the CT part number selected in the meter channel configuration? must be same.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello @Bobhow1
Can you please verify the installed CT part number and the CT part number selected in the meter channel configuration? must be same.
Regards,
Ramasamy N