PM8000 onboard PQ memory
Metering & Power Quality
  • EcoStruxure Power & Grid
  • PM8000 onboard PQ memory
Charles_Murison
Charles_Murison Champion
572
Mehran_Mehrnia
Mehran_Mehrnia Champion
209
Ramasamy_N
Ramasamy_N Champion
115
nigel_greenwave
nigel_greenwave
Mentor
Posted: ‎2019-12-10 07:01 AM
2026
How long does the waveform capture data remain visible via the web interface on a PM8000?
Charles_Murison
Champion
Posted: ‎2020-01-03 12:23 PM
2009
Hello Nigel,
Still a loaded question. For waveform recorders, data recorders and COMTrade modules, there is a limit to the depth that is hard coded. This depth limit may or may not depend on the firmware version. You could free up all the memory inside the meter and still have a depth limit. If the depths in all the modules are set such that there is free memory available then changing the setting in one or a group a modules would not affect the depth limit in a different module. However if the depths are so large that free memory is constricted then yes the depth in one or a group of modules could prevent a different module from increasing its depth.
With older ION meters like the ION7650 meter, it was fairly easy to have some modules consume most of the memory. With PM8000 and the latest firmware, this is still possible but much less likely to happen.
Replies 4
Charles_Murison
Champion
Posted: ‎2019-12-10 09:44 AM
2022
Hello Nigel,
This is a loaded question. As long as the waveforms are still in the meter. Factors like COMTRADE depth and how often waveforms are triggered are a factor.
Charles
nigel_greenwave
nigel_greenwave
Mentor
Posted: ‎2019-12-10 10:03 AM
2020
Thanks Charles,
if I decrease the size of the other logs like kWh etc, will this increase the PQ log sizes?
Charles_Murison
Champion
2010
Hello Nigel,
nigel_greenwave
nigel_greenwave
Mentor
Posted: ‎2020-01-12 09:11 PM
Thanks for your info Charles