Continue
  • My Subscriptions
  • Events
PM8000 failure
Metering & Power Quality
  • EcoStruxure Power & Grid
  • PM8000 failure
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
s2k
s2k
Explorer
Posted: ‎2022-01-04 10:57 PM . Last Modified: ‎2022-01-04 11:03 PM
1582
PM8000 failure
Hi there.
please review the below and let me have any comment to solve the problem.
Customer : Steel Company
 - Upgradede panels and replaced power meter ION6200 (or ION7330) with PM8000(8240)
 - Load type of panels which has meter not working
   - Electric furnace, Capacitor, Transformer etc.
   - In case of furnace, current fluctuates continuously
 - There has been no power meters (ION6200, iON7330) problems over 10 years
 - After upgrade we replaced nearly ten broken PM8000(8240) with new one
 - CT, PT wiring is same as before
 - Other digital devices on the same panel such as local or Simense protection relays have no problem.
   - The difference between ION6200(ION7330) : has device grounded and PM8000(8240) : has no device ground
   - Local protection relay has the same problem and they solved with device ground wiring to panel ground.
Thank you.
  • PM8000
Charles_Murison
Champion
Posted: ‎2022-01-05 08:21 AM
Hello @s2k
Strongly recommend you work with your local technical support to troubleshoot. Did not provide any details of what the problem with PM8000 is. Perhaps you are referring to phantom voltage (https://www.se.com/za/en/faqs/FAQ000133551/).
Charles
Charles_Murison
Champion
Hello @s2k
Charles