Hello everyone,
I need to ask some questions regarding the connection between real/reactive energy and
the demand real/reactive power.
For example, I know that the PM3255 meters can calculate "Active power sliding window demand delivered-received".
If you multiply this demand with the time interval for which the demand was calculated, you get active (real) energy signed
(delivered - received).
On the other hand, the PM5300 meters (particularly PM5331) calculate a parameter simply called "Demand Real Power".
I also know that the meter can show 4 types of real energy: delivered, received, signed (delivered - received), absolute
(delivered + received)
My question is this: If you multiply this "Demand Real Power" with the time interval for which the demand was calculated,
what kind of real energy would I get for PM5300? (Delivered, delivered-received, delivered+received)
Thank you for your help.
Link copied. Please paste this link to share this article on your social media post.
Hello @Janevski
The PM5300 & PM3255 power demand values are calculated based on the Delivered Energy (into the load) power values and not supported the demand calculation for Received Energy (out of load).
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello @Janevski,
I have moved your post to the metering forum.
@Ramasamy_N Would you be able to answer the question?
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
@Charles_Murison , @Ramasamy_N
Gentlemen,
Thank you very much for your time and effort to help me.
Your answers were very helpful.
Have a good day and stay safe,
Stefan Janevski.