Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

PM8000 and datacenter power quality measurement

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: PM8000 and datacenter power quality measurement
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
487
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Yarom
Lieutenant JG Yarom Lieutenant JG
Lieutenant JG

Posted: ‎2022-12-22 08:02 AM

0 Likes
2
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-22 08:02 AM

PM8000 and datacenter power quality measurement

I would like some guidance on implementing PM8000 meters for datacenter applications.

 

Where can we find a white paper, a guide or some information regarding what measurements, what features of the PM8000 and any other information that is required for monitoring of electrical supply and quality to the datacenter.

 

Client purchased and installed 4 units. Now he is at the integration state and I find that this is the point we lack in being able to support after the sale.  He is not sure himself which registers to use. We want everything that is pertinent to the proper functioning of the datacenter, the supply of electricity from the utilities and the quality of the power supplied.

 

Please send me some links or guides or communication.

 

Thanks,

 

Yarom

Labels
  • Labels:
  • PM Downloads
  • PM8000
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-01-04 09:09 AM . Last Modified: ‎2023-01-04 09:10 AM

0 Likes
1
959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-04 09:09 AM

Hello @Yarom ,

 

How is the customer connecting to the meter, software, front panel, modbus, ION, other? If software via modbus, have you had a look at the modbus map of the PM8000? The modbus mapping can be found in the firmware files for the version of firmware used by the customer. For example, for V3.1.0 firmware, the file is found in https://www.se.com/sg/en/download/document/PM8000_meter_FW_v003.001.000/  PM8000_Modbus_Map.xlsx.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Yarom
Lieutenant JG Yarom Lieutenant JG
Lieutenant JG

Posted: ‎2023-01-05 06:18 AM

0 Likes
0
947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-05 06:18 AM

Thank you @Charles_Murison ,

 

This part I am well aware of. I have the Modbus registers table, the access through ION if needed and whatever else.

 

My question regards an application expert with knowledge of Datacenter / Electrical management. The client would like to know which values (afterwhich I will look up the modbus registers) are required, what waveform to configure and any other relevant information.

 

Thanks,

 

Yarom

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of