PM8000 Sag and Swell via modbus

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Sag and Swell via modbus
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
james-wood-tel
Crewman james-wood-tel Crewman
Crewman

Posted: ‎2016-07-07 03:30 AM

0 Likes
7
1541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-07 03:30 AM

PM8000 Sag and Swell via modbus

Hi,Are we able to obtain date and time stamped info from the PM8000 as to when sag and swell occurrences occur in Modbus

Tried looking through the PM8000 modbus registers and can't find a relevant register. Is it possible to make via ION Setup

Thanks in advance

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2016-07-07 06:10 AM

0 Likes
0
1461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-07 06:10 AM

With sag / swell events in Schneider meters it is typical that you will need software to view the events.  ION Setup may give you basic data while PME will give you a better view ot the data.  I have opened ION Setup and the view for these events look pretty basic.

Sincerely,

Michael Franz

Technical Advisor

Faith Technologies.

Reply
sesa276436_brid
Ensign sesa276436_brid Ensign
Ensign

Posted: ‎2016-07-15 08:42 AM

1 Like
2
1461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-15 08:42 AM

The Pm8000 meter requires ION setup or PME to view its logs. Any logs will have the values and corresponding timestamps associated with those values.  The logs themselves would not be accessible via generic modbus read requests.

The PM8000 is programmed with ION technology, so only a limited amount of registers will be available via modbus.

Here is a link to the Modbus register map fior this device.

http://www.schneider-electric.com/cn/en/download/document/PM8000_Modbus_Map

Reply
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2016-07-19 08:16 AM

0 Likes
0
1461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-19 08:16 AM

We know how it is done.  Would like to see these values in registers.

Reply
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2016-07-26 06:51 AM

0 Likes
0
1461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-26 06:51 AM

Joshua:

I would love to see all data in Schneider meters to be open to the world.  The more open the data the easier it is to convince customers to purchase a product.  Today people with to have access to data without having to use any proprietary.  Even if the event is too high speed to place in registers while it is happening once the capture is complete if could then be placed in standard Modbus registers.  Memory is so inexpensive.  This could be done in modern devices and it would make meters more attractive to the industry.

Reply
JamesAZZO
Sisko | EcoXpert Master JamesAZZO Sisko | EcoXpert Master
Sisko | EcoXpert Master

Posted: ‎2016-07-26 07:13 AM

1 Like
1
1461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-26 07:13 AM

Log extraction of waveforms is available in open formats like comrade and iec61850 protocols in the pm8000. ION is another. 


But Modbus is not made for large data array sets like this which have no real time equivalent. That's why almost no meters have simple extraction onboard logging published. Not even the PowerLogic meters with Modbus logs. Very complex to deal with. 


Coil/Register Numbers

Data Addresses

TypeTable Name

1-9999

0000 to 270E

Read-WriteDiscrete Output Coils

10001-19999

0000 to 270E

Read-OnlyDiscrete Input Contacts

30001-39999

0000 to 270ERead-OnlyAnalog Input Registers

40001-49999

0000 to 270ERead-WriteAnalog Output Holding Registers
Reply
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2016-07-26 08:33 AM

0 Likes
0
1461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-07-26 08:33 AM

James:

To get to ComTrade you need PME to parse the file code into that form.

Having a more open front-end would be better for sales.

Thanks,

Michael

Reply
Yut
Captain Yut
Captain

Posted: ‎2017-04-19 11:18 PM

0 Likes
0
1461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-19 11:18 PM

Modbus RTU  does not support complex data like that (i.e. waveform, data log, data with timestamp) when come to PQ study native protocol like ION is the only answer. COMTRADE may serve but very limited when lot of PQ events occurred i.e lightning strike near transmission line the meter counted hundreds of events the meter cannot store hundreds of COMTRADE files.    

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of