Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000 Phase order settings

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Phase order settings
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
Koen_Rowies
Koen_Rowies Troubleshooter
Troubleshooter

Posted: ‎2018-07-05 02:23 AM

0 Likes
5
3065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-07-05 02:23 AM

PM8000 Phase order settings

Hello,

At a customer site i have 2 PM8000 devices with the phasor diagram showing an ACB rotation

When Changing the parameter via the Web interface from ABC to ACB this has no influence on the phasor diagram, shouldn’t this change then to the ABC rotation?

Second question, what happens when this parameter is not correctly set? errors in PME?

Can this parameter also be set in IONsetup? I can't find it there...

Br,

Koen

Tags (2)
  • Tags:
  • phase order
  • pm8000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Bojan
Bojan Leader
Leader

Posted: ‎2018-07-05 04:41 AM

0 Likes
0
3016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-07-05 04:41 AM

Hi Koen,

I think that Phase Order parameter is suppose to be used in Phase Reversal Unary Alarm detection, but it's not used in PM8000 like in PM5000:

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2018-07-10 03:47 PM

0 Likes
0
3016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-07-10 03:47 PM

The standard ION Setup Assistant does not expose all available registers to most users (in this case, this is a wiring issue which should of been caught during meter installation).  You can view the setup registers by switching into Advanced ION Setup view (Device Properties -> Tools -> Show Advanced Setup) and going into the Power Meter modules and modifying the appropriate setup register.

While you could start swapping polarity registers, we don't recommend this as showing "software" fixed phasors may create safety concerns when servicing the device at a later time.  Another option is you can alter the phasor rotation in ION Setup but this is a global setting which affects all phasor viewers for every device that ION Setup communicates with (Tools -> Options -> Conventions).

Reply
Bojan
Bojan Leader
Leader

Posted: ‎2018-07-11 07:33 AM

0 Likes
2
3016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-07-11 07:33 AM

Hi Koen,

Just a remark that phasing is not standardized across Distribution Systems. For three phase generation, the phase sequence and the direction of rotation must be coordinated with a local  Distribution System.

So, If you see ACB, it doesn't mean that it is a wrong phase rotation.

Best regards,

Bojan

Reply
Koen_Rowies
Koen_Rowies Troubleshooter
Troubleshooter

Posted: ‎2018-07-11 07:49 AM

0 Likes
1
3016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-07-11 07:49 AM

Hello Bojan,

Indeed this is not always in our hands, the meter is correct wired in the cabinet phase 1, 2, 3 but rotation is different sometimes. I was wondering if the phase rotation parameter has some influence on the alarms in PME. i have changed them but i don't see any difference on alarms...  If it is there it should have some reason...

Br,

Koen

Reply
Bojan
Bojan Leader
Leader

Posted: ‎2018-07-11 08:15 AM

0 Likes
0
3016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-07-11 08:15 AM

Hi Koen,

It would trigger Phase Rotation alarm in PM5000 meter if enabled, but I'm not sure for PME.

PME has configurable Alarms, but the phase rotationerror event has to be triggered by the meter, and I think PM8000 has no such alarm.

Br,

Bojan

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore