PM8000 Modbus Register and Wonderware

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Modbus Register and Wonderware
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
dice1010
dice1010
Cadet

Posted: ‎2023-02-20 10:01 AM . Last Modified: ‎2023-02-20 10:08 AM

0 Likes
3
3214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-20 10:01 AM

PM8000 Modbus Register and Wonderware

I know this is a very specific question, but I'm hoping someone can help resolve this issue. We are hoping to start pulling in information from our PM8000 to our SCADA system using wonderware. I am using the default modbus registers. I have good quality in the connection to the device but only certain tags are pulling the correct information. For instance, Current A is pulling as an integer, Current B as a Float, and Current C and Current Average are showing 0. I am attaching the setup from System Management Console. Has anyone else encountered this issue? Volts mode is setup as 4W-WYE

Attachments
Labels
  • Labels:
  • ION8000
  • PowerTag Energy
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2023-02-21 10:32 AM

0 Likes
0
3189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-21 10:32 AM

For information about Modbus register format and addressing, see the PM8000_Modbus_Map.xlsx file inside the firmware zip file.  ie. click on "PM8000 v4.0.0 Firmware and Associated Files (v4.0.0)" to download the zip file containing the documentation.
https://www.se.com/us/en/product-range/62252-powerlogic-pm8000-series/#software-and-firmware

 

ModbusRegs.png

 

See Answer In Context

Reply
Replies 3
PV_DAQ
Ensign PV_DAQ
Ensign

Posted: ‎2023-02-20 10:50 AM

0 Likes
0
3204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-20 10:50 AM

I'm a generic Modbus guy, with no Schneider specific background.

Are you sure the master is not truncating Current A to an integer value/whole number?

Are you sure the master is polling Current C and Avg current? Lots of masters intializes holding registers (the tag for data it receives) to a value of zero. If not polled, the master register shows its initialized value of zero.

Generally, when a Modbus map states registers with the leading numeral 4, as in 43000 or 43002, the registers are generally one-based addressing, starting at 40001.

Zero-based addressing is typical of hexadecimal register addresses, or index-based addresses, indexed from 0000. The setup shows that zero-based addressing checked.

If you are using one based register numbers and mixing that with zero based numbering, you might be reading and interpreting the wrong set of registers. 32 bit floating point values require two adjactent registers, for instance Current B uses 43002 and 43003.

When attempting to read 43002 and 43003, you might be off by one and getting 43001 and 43002. The word/byte order changes when that happens, but I've seen where the resulting mixed-registeer value appear to be close to what it should be, yet be incorrect.

If it were me, I'd try disabling the zero based addressing function and then do whatever is necessary to try alternative word/byte orders until something reasonable appears and whether you get full FP values.

I'd also use a generic Modbus master like Modscan or Modpoll and see what the results are with the generic.


I'm not sure what register order means, but it might be the method of word/byte swapping to get the correct order to interpret a 32 bit floating point value.

I also do not understand register size = 5 digits? What's that? A Modbus register is 16 bits.

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-02-21 08:10 AM

0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-21 08:10 AM

Hello @dice1010 ,

To expand on what PV_DAQ has said, have you tried to read the registers from the device with a modbus client other than the system you are using? https://www.se.com/ca/en/faqs/FA180037/ tester.exe for example or modbus poll, ModScan etc. The idea would be to poll registers to get the explicit 16 bit values (some modbus clients can convert these into 32 bit floating point values for you). The point is to very that device is responding to modbus polls as expected. There are also online tools that can help you convert hex numbers into floating point numbers https://www.h-schmidt.net/FloatConverter/IEEE754.html

regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2023-02-21 10:32 AM

0 Likes
0
3190
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-21 10:32 AM

For information about Modbus register format and addressing, see the PM8000_Modbus_Map.xlsx file inside the firmware zip file.  ie. click on "PM8000 v4.0.0 Firmware and Associated Files (v4.0.0)" to download the zip file containing the documentation.
https://www.se.com/us/en/product-range/62252-powerlogic-pm8000-series/#software-and-firmware

 

ModbusRegs.png

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of