Hi All,
As the title, can IM20-H show fault current instead of resistance? Thank you.
Link copied. Please paste this link to share this article on your social media post.
Hello Stuart,
IM20-H is IEC offer, the network insulation will be monitored in the form of resistance
(Ω) . Not supported in form of current measurement. The NEMA offers supports the leakage current.
Regards,
Ramasamy N