Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000 Firmware upgrade failed, now unable to recover

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Firmware upgrade failed, now unable to recover
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
JonMiles
JonMiles
Contributor

Posted: ‎2019-07-19 03:56 AM . Last Modified: ‎2022-10-19 02:51 AM

0 Likes
10
5681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-19 03:56 AM

PM8000 Firmware upgrade failed, now unable to recover

I've just been looking through the following post:

 

https://community.se.com/t5/Power-Metering/PM8000-Firmware-Issue/m-p/165386#M3455

 

I'm having the same issue i believe. I went to update to the latest FW revision (2.1.0) and something failed right at the end of the process. I've tried to downgrade the firmware to 1.4.3, also tried reapplying the 2.1.0 version, both of these fail. I get the error as you can see in the attached screenshots.

 

Device Config Checklist.JPGNAK Invalid Subservice.JPG

 

Any suggestions? I'm using the latest version of ION Setup and i believe it is not a mid meter (METSEPM8240)

 

Many thanks in advance.

Tags (4)
  • Tags:
  • failed
  • firmware
  • ion setup
  • pm8000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-08-29 08:58 AM

1 Like
1
5629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-29 08:58 AM

Hello @JonMiles,

 

The log tells me a few points.

 

A) The firmware was able to upgrade to V2.1, this is significant as this firmware cannot be downgraded. This is not a problem just a note.

B) The meters template did not get pasted onto the meter

C) The web pages did not get loaded onto the meter.

 

B and C can be addressed with individual steps.

For B:

1) Connect to the meter with ION Setup

2) In the setup assistant, navigate to template -> "Send to meter"

3) Upload the meter's template

 

For C:

1) Connect to the meter with ION Setup

2) In the setup assistant, navigate to template -> Web

3) Upload the new web pages.

 

 

 

 

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 10
Romain_Polette
Romain_Polette Champion
Champion

Posted: ‎2019-07-19 04:40 AM

3 Likes
7
5674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-19 04:40 AM

Hi @JonMiles 

 

The ION Setup Version 3.1.19143.01 has some issues while upgrading the firmware version of PM8000 to V2.1.0 using the 'Option 1: Upgrade firmware using ZIP file'. The meter gets stuck to V1.088 and displays goes blank. The latest ION Setup (3.1.19192.01) has addressed this issue. Download the latest ION Setup.

 

It worked for me with the 2 scenario :

  • Laptop and PM8000 connected in direct Ethernet
  • Laptop and PM8000 connected in serial (ION protocol) with a USB/RS485 adapter

 

Regards.

 

Romain

Romain POLETTE
Solution Architect - France Operations
Reply
JonMiles
JonMiles
Contributor

Posted: ‎2019-07-19 05:02 AM

0 Likes
6
5671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-19 05:02 AM

Thanks for your reply, @Romain_Polette 

 

I am running the latest version (downloaded this morning before trying to re update the firmware).

 

ION Setup.JPG

 

I have also tried direct Ethernet, but i haven't yet tried serial connection, however.

 

Regards

 

Jon

Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2019-07-22 03:00 PM

0 Likes
1
5664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-22 03:00 PM

Hi Jon - are you indicating you were successful with the latest ION Setup?  Thanks to clarify!


Tom

 

@Robert_Lee 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-07-22 03:42 PM

1 Like
3
5660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-22 03:42 PM

Hello @JonMiles 

 

Is it possible to get a copy of the upgrade logs? C:\ProgramData\Schneider Electric\ION Setup\Upgrade.log by default.

 

What is the meter's firmware at this time?

 

If the meter's firmware was upgraded by the template paste did not complete, it is not possible to downgrade the meter anymore. I would try manually paste the template on the meter. Same may also apply to the web pages. 

L4 Prime for Advanced metering and Utilities
Reply
Grant_IPACS
Grant_IPACS
Mentor

Posted: ‎2019-07-22 09:10 PM

0 Likes
1
5655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-22 09:10 PM

One of the guys here had a similar issue but with PM8214, it seemed to be the display firmware.

when we went from selecting all 3 files, and the 'apply pack' for the remote display this didn't work... but if we did them one at a time, it was OK.

 

Also, the few times things did crash upgrade via FTP definitely was the way to go.

 

BR

 

Grant

Regards

Grant
Reply
JonMiles
JonMiles
Contributor

Posted: ‎2019-08-29 03:47 AM

0 Likes
0
5634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-29 03:47 AM

Hi,

 

I've just tried upgrading 1 file at a time, unfortunately i get the same error - process aborted. How do you go about upgrading via FTP protocol?

 

Thanks in advance.

 

Jon

Reply
JonMiles
JonMiles
Contributor

Posted: ‎2019-08-29 03:48 AM

0 Likes
0
5633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-29 03:48 AM

Hi Tom,

 

No, unfortunately I'm still stuck with a bricked meter at the minute.

 

Jon

Reply
JonMiles
JonMiles
Contributor

Posted: ‎2019-08-29 03:56 AM

0 Likes
2
5632
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-29 03:56 AM

Hi @Charles_Murison Charles,

 

Here is a copy and paste from the Upgrade.log:

 

15:28:48: Software Version (Build): 3.1 (Build 19095)
15:28:57: Processing file: PM8000_V001.088.000.upg
15:28:57: Upgrade started at 06 June 2019 15:28:57
15:28:57: Device Name = LVB Top DR meter
15:28:57: Device Serial Number = ME-1807B333-02
15:28:57: Device IP Address = 10.10.133.12/7700
15:28:57: Device IPv6 Link Local = fe80::260:78ff:fe09:9a02
15:28:57: Device Firmware = 001.004.003
15:28:57: Upgrade Filename: PM8000_V001.088.000.upg
15:28:57: Firmware Version = 001.088.000
15:28:57: Firmware dated Mon Feb 25 12:55:44 2019
15:28:57: Device is in idle state
15:30:40: Device now in download state
15:30:40: Proceeding with firmware download
15:30:40: Transmit delay: 0 ms
15:30:40: Decreasing transmit delay: 0 ms
15:30:46: 10% completed
15:30:46: Comm efficiency = 100.0%
15:30:54: 20% completed
15:30:54: Comm efficiency = 100.0%
15:30:59: 30% completed
15:30:59: Comm efficiency = 100.0%
15:31:08: 40% completed
15:31:08: Comm efficiency = 100.0%
15:31:16: 50% completed
15:31:16: Comm efficiency = 100.0%
15:31:26: 60% completed
15:31:26: Comm efficiency = 100.0%
15:31:36: 70% completed
15:31:36: Comm efficiency = 100.0%
15:31:44: 80% completed
15:31:44: Comm efficiency = 100.0%
15:31:52: 90% completed
15:31:52: Comm efficiency = 100.0%
15:32:00: 100% completed
15:32:00: Firmware download completed
15:32:02: Disconnecting ethernet connection
15:32:02: Ethernet connection disconnected
15:33:02: Attempting to reconnect ethernet connection
15:33:42: Ethernet connection reconnected: [10.10.133.12]
15:33:48: Firmware downloaded successfully
15:33:48: Upgrade completed at 06 June 2019 15:33:48
15:33:48: Processing file: PM8000_V002.001.000.upx
15:33:48: Upgrade started at 06 June 2019 15:33:48
15:33:48: Device Name = LVB Top DR meter
15:33:48: Device Serial Number = ME-1807B333-02
15:33:48: Device IP Address = 10.10.133.12/7700
15:33:48: Device IPv6 Link Local = fe80::260:78ff:fe09:9a02
15:33:48: Device Firmware = 001.088.000
15:33:48: Upgrade Filename: PM8000_V002.001.000.upx
15:33:48: Proceeding with firmware download
15:33:48: Transmit delay: 0 ms
15:33:48: Decreasing transmit delay: 0 ms
15:33:57: 10% completed
15:33:57: Comm efficiency = 100.0%
15:34:07: 20% completed
15:34:07: Comm efficiency = 100.0%
15:34:18: 30% completed
15:34:18: Comm efficiency = 100.0%
15:34:27: 40% completed
15:34:27: Comm efficiency = 100.0%
15:34:35: 50% completed
15:34:35: Comm efficiency = 100.0%
15:34:43: 60% completed
15:34:43: Comm efficiency = 100.0%
15:34:50: 70% completed
15:34:50: Comm efficiency = 100.0%
15:34:57: 80% completed
15:34:57: Comm efficiency = 100.0%
15:35:04: 90% completed
15:35:04: Comm efficiency = 100.0%
15:35:12: 100% completed
15:35:12: Comm efficiency = 100.0%
15:35:12: Finalizing upgrade transfer
15:35:30: Installing firmware: 10%
15:35:34: Installing firmware: 20%
15:35:37: Installing firmware: 30%
15:35:41: Installing firmware: 40%
15:35:42: Installing firmware: 50%
15:35:44: Installing firmware: 60%
15:35:51: Installing firmware: 70%
15:35:58: Installing firmware: 80%
15:36:06: Installing firmware: 90%
15:36:21: Installing firmware: 100%
15:36:22: Firmware installed succesfully
15:36:22: Device restarting...
15:36:22: Disconnecting ethernet connection
15:36:22: Ethernet connection disconnected
15:37:22: Attempting to reconnect ethernet connection
15:39:02: Attempting to use IPv6 link local
15:39:11: Ethernet connection reconnected: [fe80::260:78ff:fe09:9a02]
15:39:11: Updating device connection to use IPv6 link local
15:39:13: NAK: Invalid Subservice
15:39:13: Upgrade failed at 06 June 2019 15:39:13
15:39:13: Process ended prematurely
15:39:13: Total Process Time: 10 minutes 16 seconds

 

The meters firmware is stating 2.1.0. I've logged onto the meter via FTP but all folders are empty. Same for when I log on via a web browser, it gives the "File not found" error.

 

Thanks

 

Jon

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-08-29 08:58 AM

1 Like
1
5629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-29 08:58 AM

Hello @JonMiles,

 

The log tells me a few points.

 

A) The firmware was able to upgrade to V2.1, this is significant as this firmware cannot be downgraded. This is not a problem just a note.

B) The meters template did not get pasted onto the meter

C) The web pages did not get loaded onto the meter.

 

B and C can be addressed with individual steps.

For B:

1) Connect to the meter with ION Setup

2) In the setup assistant, navigate to template -> "Send to meter"

3) Upload the meter's template

 

For C:

1) Connect to the meter with ION Setup

2) In the setup assistant, navigate to template -> Web

3) Upload the new web pages.

 

 

 

 

 

L4 Prime for Advanced metering and Utilities
Reply
JonMiles
JonMiles
Contributor

Posted: ‎2019-08-30 02:01 AM

0 Likes
0
5626
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-30 02:01 AM

@Charles_Murison

 

I can confirm this has restored the meter pages and all seems to be working correctly again now. Thank you very much for the assistance. Using your instructions it was so easy and straight forward.

 

Regards

 

Jon

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore