Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82179members
349777posts

Present Demand value caclutaion at Sliding Block method in EM7280

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

varad
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
8
494

Present Demand value caclutaion at Sliding Block method in EM7280

Hi,

I have installed the EM7280 at customers site for demand controlling application.

Chosen the Auto Demand calculation method for KVA at period of 15 mins. The KVA trend at site is nearly constant, ranges from 9.2 MVA to 9.6 MVA.

As the calculation method is Auto(Sliding Window) we are suspecting that the present demand value should be in the same range as the KVA trend.

But at some instance of time, present demand falls down to 0.9 - 1.2 MVA.

Please help me to understand this so that I would be able to further explain to customer.

 

 

 

8 Replies 8
Ramasamy_N
Commander Commander
Commander
0 Likes
7
483

Re: Present Demand value caclutaion at Sliding Block method in EM7280

Hello, 

 

The present demand value will be calculated and updated at the interval of 15 seconds for auto black in EM7280. If there is any change in power values, there will be change in present demand value also. Please check the power values when the present demand is falling to  0.9 - 1.2 MVA.

 

Regards, 

Ramasamy N

varad
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
6
479

Re: Present Demand value caclutaion at Sliding Block method in EM7280

Hi,

 

Yes its correct about update time for values, but we have checked the power (KVA) is as same ranges 9.0 - 9.5 MVA even though the present Demand shows 0.9 - 1.5 MVA.

 

Ramasamy_N
Commander Commander
Commander
0 Likes
5
469

Re: Present Demand value caclutaion at Sliding Block method in EM7280

Hi, 

Ok, if the power values are constant the present demand will be same as last demand for all the interval. one possible cause for drop in the present demand (start from 0VA) will be device power OFF. Is the EM7280 power cycled ?

 

Regards, 

Ramasamy N

varad
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
4
461

Re: Present Demand value caclutaion at Sliding Block method in EM7280

Hi Ram,

 

Device supposed to be continuously on. This fall down occurs frequently so lets check out this possibility.

 

Is the EM7280 power cycled ? I cant understand what this means? Is it any setting to be done for this?

 

Ramasamy_N
Commander Commander
Commander
0 Likes
3
459

Re: Present Demand value caclutaion at Sliding Block method in EM7280

Hi, 

I was asking about, is the  EM7280 powered OFF before the present demand fall down?

If not, please log the power and present demand parameters using any Modbus application (with interval of 5 to 10 seconds) and share the data for further analysis.

 

Regards, 

Ramasamy N

varad
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
2
457

Re: Present Demand value caclutaion at Sliding Block method in EM7280

Hi Ram

 

We have checked the power off with EM 7230 at my lab, The present Demand value does not reset after power off.

 

Please find attachments from customer about block demand. It seems after every 1 hour the present demand resets.

Attachments
Ramasamy_N
Commander Commander
Commander
0 Likes
1
448

Re: Present Demand value caclutaion at Sliding Block method in EM7280

Hi, 

Sorry for the delay in reply, 

Thanks for the details, we are analyzing this issue will keep you posted. 

 

Regards, 

Ramasamy N

varad
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
0
445

Re: Present Demand value caclutaion at Sliding Block method in EM7280

Hi

 

Further more we have observed that this interval demand parameter goes to 0 after every hour. That means at every 33rd minute from hours the demand parameter goes to 0.

 

Is it the auto reset?