Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Present Demand value caclutaion at Sliding Block method in EM7280

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Present Demand value caclutaion at Sliding Block method in EM7280
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
varad
varad
Contributor

Posted: ‎2019-08-07 10:45 PM

0 Likes
8
3135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-07 10:45 PM

Present Demand value caclutaion at Sliding Block method in EM7280

Hi,

I have installed the EM7280 at customers site for demand controlling application.

Chosen the Auto Demand calculation method for KVA at period of 15 mins. The KVA trend at site is nearly constant, ranges from 9.2 MVA to 9.6 MVA.

As the calculation method is Auto(Sliding Window) we are suspecting that the present demand value should be in the same range as the KVA trend.

But at some instance of time, present demand falls down to 0.9 - 1.2 MVA.

Please help me to understand this so that I would be able to further explain to customer.

 

 

 

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2019-08-13 03:07 AM

0 Likes
7
3123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-13 03:07 AM

Hello, 

 

The present demand value will be calculated and updated at the interval of 15 seconds for auto black in EM7280. If there is any change in power values, there will be change in present demand value also. Please check the power values when the present demand is falling to  0.9 - 1.2 MVA.

 

Regards, 

Ramasamy N

Reply
varad
varad
Contributor

Posted: ‎2019-08-13 07:52 PM

0 Likes
6
3119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-13 07:52 PM

Hi,

 

Yes its correct about update time for values, but we have checked the power (KVA) is as same ranges 9.0 - 9.5 MVA even though the present Demand shows 0.9 - 1.5 MVA.

 

Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2019-08-13 09:26 PM

0 Likes
5
3109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-13 09:26 PM

Hi, 

Ok, if the power values are constant the present demand will be same as last demand for all the interval. one possible cause for drop in the present demand (start from 0VA) will be device power OFF. Is the EM7280 power cycled ?

 

Regards, 

Ramasamy N

Reply
varad
varad
Contributor

Posted: ‎2019-08-15 09:18 PM

0 Likes
4
3101
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-15 09:18 PM

Hi Ram,

 

Device supposed to be continuously on. This fall down occurs frequently so lets check out this possibility.

 

Is the EM7280 power cycled ? I cant understand what this means? Is it any setting to be done for this?

 

Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2019-08-16 03:58 AM

0 Likes
3
3099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-16 03:58 AM

Hi, 

I was asking about, is the  EM7280 powered OFF before the present demand fall down?

If not, please log the power and present demand parameters using any Modbus application (with interval of 5 to 10 seconds) and share the data for further analysis.

 

Regards, 

Ramasamy N

Reply
varad
varad
Contributor

Posted: ‎2019-08-16 04:57 AM

0 Likes
2
3097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-16 04:57 AM

Hi Ram

 

We have checked the power off with EM 7230 at my lab, The present Demand value does not reset after power off.

 

Please find attachments from customer about block demand. It seems after every 1 hour the present demand resets.

Attachments
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2019-08-29 09:18 AM

0 Likes
1
3088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-29 09:18 AM

Hi, 

Sorry for the delay in reply, 

Thanks for the details, we are analyzing this issue will keep you posted. 

 

Regards, 

Ramasamy N

Reply
varad
varad
Contributor

Posted: ‎2019-08-29 09:03 PM

0 Likes
0
3085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-29 09:03 PM

Hi

 

Further more we have observed that this interval demand parameter goes to 0 after every hour. That means at every 33rd minute from hours the demand parameter goes to 0.

 

Is it the auto reset?

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore