Present Demand value caclutaion at Sliding Block method in EM7280

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Present Demand value caclutaion at Sliding Block method in EM7280
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
varad
Lieutenant | EcoXpert Master varad Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-08-07 10:45 PM

0 Likes
8
1639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-07 10:45 PM

Present Demand value caclutaion at Sliding Block method in EM7280

Hi,

I have installed the EM7280 at customers site for demand controlling application.

Chosen the Auto Demand calculation method for KVA at period of 15 mins. The KVA trend at site is nearly constant, ranges from 9.2 MVA to 9.6 MVA.

As the calculation method is Auto(Sliding Window) we are suspecting that the present demand value should be in the same range as the KVA trend.

But at some instance of time, present demand falls down to 0.9 - 1.2 MVA.

Please help me to understand this so that I would be able to further explain to customer.

 

 

 

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2019-08-13 03:07 AM

0 Likes
7
1627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-13 03:07 AM

Hello, 

 

The present demand value will be calculated and updated at the interval of 15 seconds for auto black in EM7280. If there is any change in power values, there will be change in present demand value also. Please check the power values when the present demand is falling to  0.9 - 1.2 MVA.

 

Regards, 

Ramasamy N

Reply
varad
Lieutenant | EcoXpert Master varad Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-08-13 07:52 PM

0 Likes
6
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-13 07:52 PM

Hi,

 

Yes its correct about update time for values, but we have checked the power (KVA) is as same ranges 9.0 - 9.5 MVA even though the present Demand shows 0.9 - 1.5 MVA.

 

Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2019-08-13 09:26 PM

0 Likes
5
1613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-13 09:26 PM

Hi, 

Ok, if the power values are constant the present demand will be same as last demand for all the interval. one possible cause for drop in the present demand (start from 0VA) will be device power OFF. Is the EM7280 power cycled ?

 

Regards, 

Ramasamy N

Reply
varad
Lieutenant | EcoXpert Master varad Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-08-15 09:18 PM

0 Likes
4
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-15 09:18 PM

Hi Ram,

 

Device supposed to be continuously on. This fall down occurs frequently so lets check out this possibility.

 

Is the EM7280 power cycled ? I cant understand what this means? Is it any setting to be done for this?

 

Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2019-08-16 03:58 AM

0 Likes
3
1603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-16 03:58 AM

Hi, 

I was asking about, is the  EM7280 powered OFF before the present demand fall down?

If not, please log the power and present demand parameters using any Modbus application (with interval of 5 to 10 seconds) and share the data for further analysis.

 

Regards, 

Ramasamy N

Reply
varad
Lieutenant | EcoXpert Master varad Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-08-16 04:57 AM

0 Likes
2
1601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-16 04:57 AM

Hi Ram

 

We have checked the power off with EM 7230 at my lab, The present Demand value does not reset after power off.

 

Please find attachments from customer about block demand. It seems after every 1 hour the present demand resets.

Attachments
Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2019-08-29 09:18 AM

0 Likes
1
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-29 09:18 AM

Hi, 

Sorry for the delay in reply, 

Thanks for the details, we are analyzing this issue will keep you posted. 

 

Regards, 

Ramasamy N

Reply
varad
Lieutenant | EcoXpert Master varad Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-08-29 09:03 PM

0 Likes
0
1589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-29 09:03 PM

Hi

 

Further more we have observed that this interval demand parameter goes to 0 after every hour. That means at every 33rd minute from hours the demand parameter goes to 0.

 

Is it the auto reset?

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of