PM8000 Firmware upgrade failed, now unable to recover

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
JonMiles
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
10
1008

PM8000 Firmware upgrade failed, now unable to recover

I've just been looking through the following post:

 

https://community.exchange.se.com/t5/Power-Metering/PM8000-Firmware-Issue/m-p/165386#M3455

 

I'm having the same issue i believe. I went to update to the latest FW revision (2.1.0) and something failed right at the end of the process. I've tried to downgrade the firmware to 1.4.3, also tried reapplying the 2.1.0 version, both of these fail. I get the error as you can see in the attached screenshots.

 

Device Config Checklist.JPGNAK Invalid Subservice.JPG

 

Any suggestions? I'm using the latest version of ION Setup and i believe it is not a mid meter (METSEPM8240)

 

Many thanks in advance.


Accepted Solutions
Charles_Murison
Picard Picard
Picard

Re: PM8000 Firmware upgrade failed, now unable to recover

Hello @JonMiles,

 

The log tells me a few points.

 

A) The firmware was able to upgrade to V2.1, this is significant as this firmware cannot be downgraded. This is not a problem just a note.

B) The meters template did not get pasted onto the meter

C) The web pages did not get loaded onto the meter.

 

B and C can be addressed with individual steps.

For B:

1) Connect to the meter with ION Setup

2) In the setup assistant, navigate to template -> "Send to meter"

3) Upload the meter's template

 

For C:

1) Connect to the meter with ION Setup

2) In the setup assistant, navigate to template -> Web

3) Upload the new web pages.

 

 

 

 

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

10 Replies 10
Romain_Polette
Sisko Sisko
Sisko

Re: PM8000 Firmware upgrade failed, now unable to recover

Hi @JonMiles 

 

The ION Setup Version 3.1.19143.01 has some issues while upgrading the firmware version of PM8000 to V2.1.0 using the 'Option 1: Upgrade firmware using ZIP file'. The meter gets stuck to V1.088 and displays goes blank. The latest ION Setup (3.1.19192.01) has addressed this issue. Download the latest ION Setup.

 

It worked for me with the 2 scenario :

  • Laptop and PM8000 connected in direct Ethernet
  • Laptop and PM8000 connected in serial (ION protocol) with a USB/RS485 adapter

 

Regards.

 

Romain

Romain POLETTE - Solution architect - France Operation
Intencity - Grenoble - France
JonMiles
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
6
1001

Re: PM8000 Firmware upgrade failed, now unable to recover

Thanks for your reply, @Romain_Polette 

 

I am running the latest version (downloaded this morning before trying to re update the firmware).

 

ION Setup.JPG

 

I have also tried direct Ethernet, but i haven't yet tried serial connection, however.

 

Regards

 

Jon

Tom_Stevenson
Picard Picard
Picard
0 Likes
1
994

Re: PM8000 Firmware upgrade failed, now unable to recover

Hi Jon - are you indicating you were successful with the latest ION Setup?  Thanks to clarify!


Tom

 

@Robert_Lee 

Charles_Murison
Picard Picard
Picard

Re: PM8000 Firmware upgrade failed, now unable to recover

Hello @JonMiles 

 

Is it possible to get a copy of the upgrade logs? C:\ProgramData\Schneider Electric\ION Setup\Upgrade.log by default.

 

What is the meter's firmware at this time?

 

If the meter's firmware was upgraded by the template paste did not complete, it is not possible to downgrade the meter anymore. I would try manually paste the template on the meter. Same may also apply to the web pages. 

L4 Prime for Advanced metering and Utilities
Grant_IPACS
Commander
Commander
0 Likes
1
985

Re: PM8000 Firmware upgrade failed, now unable to recover

One of the guys here had a similar issue but with PM8214, it seemed to be the display firmware.

when we went from selecting all 3 files, and the 'apply pack' for the remote display this didn't work... but if we did them one at a time, it was OK.

 

Also, the few times things did crash upgrade via FTP definitely was the way to go.

 

BR

 

Grant

Regards

Grant
JonMiles
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
0
964

Re: PM8000 Firmware upgrade failed, now unable to recover

Hi,

 

I've just tried upgrading 1 file at a time, unfortunately i get the same error - process aborted. How do you go about upgrading via FTP protocol?

 

Thanks in advance.

 

Jon

JonMiles
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
0
963

Re: PM8000 Firmware upgrade failed, now unable to recover

Hi Tom,

 

No, unfortunately I'm still stuck with a bricked meter at the minute.

 

Jon

JonMiles
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
2
962

Re: PM8000 Firmware upgrade failed, now unable to recover

Hi @Charles_Murison Charles,

 

Here is a copy and paste from the Upgrade.log:

 

15:28:48: Software Version (Build): 3.1 (Build 19095)
15:28:57: Processing file: PM8000_V001.088.000.upg
15:28:57: Upgrade started at 06 June 2019 15:28:57
15:28:57: Device Name = LVB Top DR meter
15:28:57: Device Serial Number = ME-1807B333-02
15:28:57: Device IP Address = 10.10.133.12/7700
15:28:57: Device IPv6 Link Local = fe80::260:78ff:fe09:9a02
15:28:57: Device Firmware = 001.004.003
15:28:57: Upgrade Filename: PM8000_V001.088.000.upg
15:28:57: Firmware Version = 001.088.000
15:28:57: Firmware dated Mon Feb 25 12:55:44 2019
15:28:57: Device is in idle state
15:30:40: Device now in download state
15:30:40: Proceeding with firmware download
15:30:40: Transmit delay: 0 ms
15:30:40: Decreasing transmit delay: 0 ms
15:30:46: 10% completed
15:30:46: Comm efficiency = 100.0%
15:30:54: 20% completed
15:30:54: Comm efficiency = 100.0%
15:30:59: 30% completed
15:30:59: Comm efficiency = 100.0%
15:31:08: 40% completed
15:31:08: Comm efficiency = 100.0%
15:31:16: 50% completed
15:31:16: Comm efficiency = 100.0%
15:31:26: 60% completed
15:31:26: Comm efficiency = 100.0%
15:31:36: 70% completed
15:31:36: Comm efficiency = 100.0%
15:31:44: 80% completed
15:31:44: Comm efficiency = 100.0%
15:31:52: 90% completed
15:31:52: Comm efficiency = 100.0%
15:32:00: 100% completed
15:32:00: Firmware download completed
15:32:02: Disconnecting ethernet connection
15:32:02: Ethernet connection disconnected
15:33:02: Attempting to reconnect ethernet connection
15:33:42: Ethernet connection reconnected: [10.10.133.12]
15:33:48: Firmware downloaded successfully
15:33:48: Upgrade completed at 06 June 2019 15:33:48
15:33:48: Processing file: PM8000_V002.001.000.upx
15:33:48: Upgrade started at 06 June 2019 15:33:48
15:33:48: Device Name = LVB Top DR meter
15:33:48: Device Serial Number = ME-1807B333-02
15:33:48: Device IP Address = 10.10.133.12/7700
15:33:48: Device IPv6 Link Local = fe80::260:78ff:fe09:9a02
15:33:48: Device Firmware = 001.088.000
15:33:48: Upgrade Filename: PM8000_V002.001.000.upx
15:33:48: Proceeding with firmware download
15:33:48: Transmit delay: 0 ms
15:33:48: Decreasing transmit delay: 0 ms
15:33:57: 10% completed
15:33:57: Comm efficiency = 100.0%
15:34:07: 20% completed
15:34:07: Comm efficiency = 100.0%
15:34:18: 30% completed
15:34:18: Comm efficiency = 100.0%
15:34:27: 40% completed
15:34:27: Comm efficiency = 100.0%
15:34:35: 50% completed
15:34:35: Comm efficiency = 100.0%
15:34:43: 60% completed
15:34:43: Comm efficiency = 100.0%
15:34:50: 70% completed
15:34:50: Comm efficiency = 100.0%
15:34:57: 80% completed
15:34:57: Comm efficiency = 100.0%
15:35:04: 90% completed
15:35:04: Comm efficiency = 100.0%
15:35:12: 100% completed
15:35:12: Comm efficiency = 100.0%
15:35:12: Finalizing upgrade transfer
15:35:30: Installing firmware: 10%
15:35:34: Installing firmware: 20%
15:35:37: Installing firmware: 30%
15:35:41: Installing firmware: 40%
15:35:42: Installing firmware: 50%
15:35:44: Installing firmware: 60%
15:35:51: Installing firmware: 70%
15:35:58: Installing firmware: 80%
15:36:06: Installing firmware: 90%
15:36:21: Installing firmware: 100%
15:36:22: Firmware installed succesfully
15:36:22: Device restarting...
15:36:22: Disconnecting ethernet connection
15:36:22: Ethernet connection disconnected
15:37:22: Attempting to reconnect ethernet connection
15:39:02: Attempting to use IPv6 link local
15:39:11: Ethernet connection reconnected: [fe80::260:78ff:fe09:9a02]
15:39:11: Updating device connection to use IPv6 link local
15:39:13: NAK: Invalid Subservice
15:39:13: Upgrade failed at 06 June 2019 15:39:13
15:39:13: Process ended prematurely
15:39:13: Total Process Time: 10 minutes 16 seconds

 

The meters firmware is stating 2.1.0. I've logged onto the meter via FTP but all folders are empty. Same for when I log on via a web browser, it gives the "File not found" error.

 

Thanks

 

Jon

Charles_Murison
Picard Picard
Picard

Re: PM8000 Firmware upgrade failed, now unable to recover

Hello @JonMiles,

 

The log tells me a few points.

 

A) The firmware was able to upgrade to V2.1, this is significant as this firmware cannot be downgraded. This is not a problem just a note.

B) The meters template did not get pasted onto the meter

C) The web pages did not get loaded onto the meter.

 

B and C can be addressed with individual steps.

For B:

1) Connect to the meter with ION Setup

2) In the setup assistant, navigate to template -> "Send to meter"

3) Upload the meter's template

 

For C:

1) Connect to the meter with ION Setup

2) In the setup assistant, navigate to template -> Web

3) Upload the new web pages.

 

 

 

 

 

L4 Prime for Advanced metering and Utilities
JonMiles
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
0
956

Re: PM8000 Firmware upgrade failed, now unable to recover

@Charles_Murison

 

I can confirm this has restored the meter pages and all seems to be working correctly again now. Thank you very much for the assistance. Using your instructions it was so easy and straight forward.

 

Regards

 

Jon