Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000 DCF FIle for standard meter type

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 DCF FIle for standard meter type
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
swil
swil
Mentor

Posted: ‎2022-05-02 06:17 AM

0 Likes
5
3157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-02 06:17 AM

PM8000 DCF FIle for standard meter type

There is a standard meter framework in place on a site. It is running in a PM8000 with FAC1 Revision 3.0.0 and FAC1 Template 8000 V2.2.0.0.0.

 

I have a dcf file and will have no issues replicating the configuration to meters with the same firmware and template versions.

 

But what happens when applying this dcf file when it becomes older and:

1. New meters are shipped with firmware upgrades, e.g. a minor or major revision?

2. Template upgrades occur (are these just overwritten by the 'old' dcf file?)

 

 

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2022-05-02 08:30 AM

0 Likes
4
3150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-02 08:30 AM

Hi

 

Updated templates are not always part of a new release as you are observing with V3.0.0 firmware (which continued to use the V2.2.0.0.0), but the V3.1.0 firmware release had an updated V3.1.0.0.0 framework companion which had some fixes in it.

 

So new PM8000s ship with V3.1.0 firmware and a V3.1.0.0.0 framework.  If you were to apply a V2.2.0.0.0 framework or template to it, in most cases it should work, however, it may not have all the latest features or fixes.


Tom

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 5
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2022-05-02 08:30 AM

0 Likes
4
3150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-02 08:30 AM

Hi

 

Updated templates are not always part of a new release as you are observing with V3.0.0 firmware (which continued to use the V2.2.0.0.0), but the V3.1.0 firmware release had an updated V3.1.0.0.0 framework companion which had some fixes in it.

 

So new PM8000s ship with V3.1.0 firmware and a V3.1.0.0.0 framework.  If you were to apply a V2.2.0.0.0 framework or template to it, in most cases it should work, however, it may not have all the latest features or fixes.


Tom

Tags (1)
  • Tags:
  • english
Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2022-05-02 08:32 AM

0 Likes
2
3148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-02 08:32 AM

Just a reminder as well that as of V3.1.0, factory frameworks are provided in framework (.fwn) format, not .dcf.

 

Tom

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-05-03 01:36 PM . Last Modified: ‎2022-05-03 01:36 PM

1 Like
0
3118
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-03 01:36 PM

Hello @swil ,

 

To expand on Tom's reply in the vast majority of cases newer firmware is able to support older frameworks. This is not explicitly tested for each release. There may be a future version of firmware that does not support module X (see sunsetting post in the forum), if your old template had this module you may not be able to post this onto a new firmware. Tools used to post the framework may or may not be smart enough to avoid trying to send those modules to the meter during paste.

 

There is also the possibility that some setting did not exist in the old firmware version that is required in the new firmware. There is a default settings that will be chosen but depending on what was in the old template this could the template to either not paste or paste but not have all modules online at the end.

I would like to say again that these are extreme edge cases and usually involve highly customized frameworks. As long as the frameworks are not too old, you should be able to paste older frameworks onto newer firmware. But as noted by Tom, the newer firmware sometimes has fixes inside the template that will not been seen if you use an older template. 

 

In general I recommend A) Keeping a backup of any customized template, and if possible and reasonable, document the changes made so that these changes can be applied to future templates.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
swil
swil
Mentor

Posted: ‎2022-05-04 03:52 PM

0 Likes
1
3097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-04 03:52 PM

Thanks @Tom_Stevenson .

 

Can entire PM8000 meters with firmware greater than V2.0 be copied by selecting the entire meter and saving it as a fwn file? (then lock pasting in the next meter - ignoring 'edge cases' referred to by Charles where module types are retired.

 

If .dcf files aren't released, will those using only ION Setup (not designer) be able to apply .fwn files to meters from V3.1 firmware onwards?

 

 

Tags (1)
  • Tags:
  • english
Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2022-05-04 04:03 PM . Last Modified: ‎2022-10-19 12:54 AM

0 Likes
0
3095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-04 04:03 PM

Fwn files work with ION Designer and ION Setup, so there are no compatibility issues (https://community.se.com/t5/Metering-Power-Quality/PowerOfION-ION-Frameworks-Part-1-Framework-File-F...)

 

PME has V2.2.0.0.0 framework (.fwn) files included with it too, so there is no need to create fwn files.

 

Tom

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore