Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

【PM5560】Starting Current and Accuracy of PM5560

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • 【PM5560】Starting Current and Accuracy of PM5560
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
570
Mehran_Mehrnia
Mehran_Mehrnia Champion
202
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Miyai
Miyai
Contributor

Posted: ‎2023-07-05 07:26 PM

0 Likes
4
1704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-05 07:26 PM

【PM5560】Starting Current and Accuracy of PM5560

Hello 

 

 

I need advice on whether my understanding of the current measurement of PM5560 is correct.

 

The minimum value for current measurement is 5 mA.

However, 5-49mA cannot guarantee the specified accuracy.

The range in which the accuracy of the specified can be maintained is from 50 mA to 10 A.

 

Is the above idea correct?

I would like to confirm the above as the explanation differs from the ION9000 and other manuals.

 

Miyai_0-1688610298117.png

 

 

Best regards,

Miyai

Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2023-07-07 02:15 AM

1 Like
1
1669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-07 02:15 AM

Hi @Miyai 

The PM5500 starting current is 0.1% of nominal current (5mA) which will not claim any accuracy for this range 0.1% to 1%. (5mA to 50mA) in the standards like IEC62053-22 that we comply. 

Ramasamy_N_0-1688721238201.png

The 50mA to 250mA test points will have ±0.4% allowed error even for Class 0.2 meters. 

 

Regards, 

Ramasamy N 

See Answer In Context

Reply
Replies 4
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-07-06 09:51 AM

0 Likes
1
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-06 09:51 AM

Hello @Miyai ,

 

When you say "explanation differs from the ION9000 and other manuals." What in particular are you referring to in the ION9000 manual?

 

If you are saying the starting current for ION9000 is different than PM5560, this could be explained that these are different meters with different nominal currents.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Miyai
Miyai
Contributor

Posted: ‎2023-07-06 05:02 PM

0 Likes
0
1681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-06 05:02 PM

Hello @Charles_Murison 

 

ION9000 manual was described below.

I understand because the ”accuracy range” is clearly stated.

Miyai_0-1688687215751.png

 

However, I do not understand exactly what the PM5500 manual describes.

Is it correct to assume that the area marked below is the accuracy range?

Miyai_1-1688687423071.png

 

I would like to confirm this just to be sure, as I have received an inquiry from a client.

 

Best regards,

Miyai

Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2023-07-07 02:15 AM

1 Like
1
1670
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-07 02:15 AM

Hi @Miyai 

The PM5500 starting current is 0.1% of nominal current (5mA) which will not claim any accuracy for this range 0.1% to 1%. (5mA to 50mA) in the standards like IEC62053-22 that we comply. 

Ramasamy_N_0-1688721238201.png

The 50mA to 250mA test points will have ±0.4% allowed error even for Class 0.2 meters. 

 

Regards, 

Ramasamy N 

Reply
Miyai
Miyai
Contributor

Posted: ‎2023-07-11 05:15 PM

0 Likes
0
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-11 05:15 PM

Hi @Ramasamy_N 

 

I understand.
Thanks for your advice.

 

 

Best regards,

Miyai

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore